Hi everyone,
Bought some Flexi meter tailes from a supplier today , Am I going crazy or that I marked up incorrect . The Flexi tiles I’m used to has 19 strands of copper or similar, opposed to the normal six or seven.
The ones I’ve got today, Looked like finally stranded wire, at least 200 strands. (I didn’t count them all but that looks about right).
Correct me if I’m wrong but I’m pretty sure these a tri rated cables, And not meant to be used as standard meter tiles.
Checked on the cable and it’s marked up as 6181Y, so the code is correct.
Haven’t used them yet, Once everyone think of these as meter tailes ?? And yes they are double insulated or insulated and sheathed singles.
??
 
Odd, any idea of the maker?

The issue with fine stranded wire ia (a) you should use a ferrule, and (b) most DNO do not approve them for connection to the cut-out or meter terminals.
 
Odd, any idea of the maker?

The issue with fine stranded wire ia (a) you should use a ferrule, and (b) most DNO do not approve them for connection to the cut-out or meter terminals.
The brand on the cable says Dikkan, just had a look closer and Don’t know if it’s been printed correct or not as it says 6181Y, then further along the cable it says 6381Y!!
Thanks for that as well, thought I boot lace feral would be needed, And didn’t know about that with the DNO, Has never had these before.
Looks like it’s going to be a return to them tomorrow, They’ll be happy as they were cut to length ??
 
Sounds like you may have 6381Y and not 6181Y, are you sure you aren't misreading it.
Edit: we posted at the same time.
 
I have has similar before, ordered tails, got some blue in 6181Y and brown in 6381Y.
not amused when i went to fit them.
 
It looks handy stuff for some jobs, but just not what you wanted!

Last time I needed something I just got the Doncaster Easi-Fitl kit from Toolstation as it was in stock and only minutes away.
 
It looks handy stuff for some jobs, but just not what you wanted!

Last time I needed something I just got the Doncaster Easi-Fitl kit from Toolstation as it was in stock and only minutes away.
Exactly that’s it , not worth a call back because of using wrong cable , ...
not used the Doncaster kit before , just checked it out at toolstation .. they look good , will remember for next time .
thanks mr PC ?
 

Reply to Tri rated meter tails or flexible meter tails in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I don't know if I should ask it here or the main electricians forum. It's about CU change and the work around it and the CU change will be done...
Replies
78
Views
11K
Hi guys can anyone help, few of the sparks over here in jersey are using 25mm double insulated flexible (15-16 strands) at supply intake for...
Replies
8
Views
2K
Hi everyone, hope you’re all doing well. Got a job starting next week for a rewire of a studio flat, currently they have 10 mm T&E as metre tails...
Replies
9
Views
7K
Can the hive mind tell me where I can source the meter tail grommets that pack a 16mm insulated/sheathed tail up to 25mm? The Henley block...
Replies
9
Views
3K
Hello everyone, I have recently qualified, though yet to start practising, as an electrician. I have noticed, at my home, the tails from the...
Replies
20
Views
11K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock