mbow

Hi everyone,

I have a crabtree consumer unit with the old Crabtree C50 MCBs in it. The lighting circuit is a riing on a 7.5A MCB, 1.5mm cable and services 6 bathroom spots, 6 lights and 2 outside security lights.

The problem is that the mcb trips after 20 minutes or so. this is when only a couple of lights are used so demand isnt high. It even trips when no lights are on!! I have tried isolating the problem to specific lights but it trips randomly.

One thing I have noticed is i have rock wool insulation over the cables in the ceiling void. Can this be heating the cables up??

Can anyone give me an idea of what could be causing it to trip?

Thanks
 
unusual circuit there.
if it aint overload then its eart fault developing over time,
have you tested the cables , removed fittings and done a visual?
 
If it's not overloaded and IR tests are good it may be a worn out MCB.....try changing it for one of the same rating and type....a clamp meter will also be useful to check the current being drawn.
 
I have had similar problems a few times before, its always been a problem in one of the lights, generally insulation breaking down after a while, or a fault in a PIR, or a transformer.

Ian
 
There could also be moisture ingress in the outside lights, so if after checking internal light fittings and changing MCB the fault still exists then you could isolate the eternal lights as a test to determine if the problem is indoor or outdoors. Also another thing to bear in mind is that you should make no assumptions about the wiring of a property especially old wiring. It is not unheard of for DIY and other trades to tap off from lighting circuits to use as a socket outlet somewhere in the house.
 

Reply to Tripping MCB after 20 mins in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
614
I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K
Can i just check something. If a rat decides to chew a cable will it trip the MCB or RCD ? I ask because I had one house recently that had a...
Replies
10
Views
2K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock