Hi all,

Would it be possible to get a little advise from the guys.
I have today been to look at a job whereas there is a TT earthing arrangement with no 100ma time delayed RCD on the incoming tails so that is the first thing that needs to be done but the question is, the existing CU has a 30ma main switch RCD. Am I correct to think that this should be changed for a split board with 2 RCD's as well as the installation of the main 100ma RCD. All advice is appreciated.
Cheers
 
Some people replace the consumer main switch with a 100ma RCD the last one I did, I didn't bother and it was used in an assessment visit and they were happy about it. Also speaking to NICEIC help line they also seem to think it is ok without.
 
I was asked to take a look as a British Gas engineer had pointed out a couple of issues.
1/ No 100ma RCD before the CU.
2/ does the consumer unit need changing to meet regs

I have been out to the property this evening and I have seen that there is no time delayed RCD and there is only 1 30ma RCD on the whole CU.
I haven't quoted anything yet as I want to make sure that I advise the customer properly so I am not doing work that is unnecessary and also charging the customer for this work also. I'm no cowboy.
So my main concern is that it only has 1 RCD in the CU.
should this have a split board or is the existing board ok as long as I put the 100ma RCD on there.
I suppose I could even swap out the existing main switch and replace it with a double pole RCD.
 
It doesn't sound like anything needs to be done from your description. Section 3 of the on site guide gives suggested consumer unit arrangements. Having one 30mA RCD covering all circuits is not very convenient. But during an inspection I would only note it down as a code 3. I certainly wouldn't be concerned in this scenario. Why is a 100mA RCD required before the 30mA RCD main switch? Is the consumer unit remote from the supply position?
 
Thanks Guys,
Well, maybe the british gas engineer and my understanding of a TT arrangement are misunderstood as I was under the impression that a TT arrangement required a 100ma RCD.
 
If you are doing a fuseboard change, or a new install then you would adopt, perhaps, a different approach.

Going round advising people to update CU's is simply going to alienate potential customers.

FWIW there are so many homes, on TT supplies, with good old BS3036 CU's...
 
If you are doing a fuseboard change, or a new install then you would adopt, perhaps, a different approach.

Going round advising people to update CU's is simply going to alienate potential customers.

FWIW there are so many homes, on TT supplies, with good old BS3036 CU's...

I have done work on TT supplies with the good old BS3036 CU's and all have 100ma RCD's installed before the board.
That's the reason I am asking besides the fact that the BG engineer said the same thing.
 
So, if I can just get this straight. the BG engineer is incorrect and no work is required as the CU is protected by a 30ma RCD.
Yes. Before Amm 3 of BS7671 if you used a CU with a metal enclosure on a TT it was frowned upon and a separate rcd could be fitted to provide fault protection to the enclosure.
 

Reply to TT earthing arrangment and CU in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
860
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
523
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
Im starting a re-wire of a top floor flat, they have run an 16mm T&E with a 6mm earth from the ground floor to the 3rd floor feeding the CU...
Replies
18
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock