Discuss TT eicr code? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

If you have a fault where the resistance is between 7660Ω and 2300Ω then the RCD would (probably) not trip in <0.2 s however it is not required to according to BS7671. This would be a similar situation to MCBs that will not trip in the required time if the fault current is low; similarly how do you know and MCB will trip in the time stated, you do not know, you are relying on the manufacturers making them to standard. It is not (in standard situations) safe to test this compliance.

You are quite right, however we still record the disconnection time on a 100mA at 1x and 1x only. This is the disconnection time at its rated current, which is higher than 200ms, therefore it will not comply.
 
You are quite right, however we still record the disconnection time on a 100mA at 1x and 1x only. This is the disconnection time at its rated current, which is higher than 200ms, therefore it will not comply.
There is a difference between the requirements to meet disconnection times and the requirements to test if the RCD functions.
The disconnection times would be met so long as the Zs reading complied.
The 100mA time delayed RCD tripping in >130ms<500ms at Idn shows that it is working.
 
OK I think I am at a loss to explain here.
The disconnection time of 0.2s for a fault of negligible impedance, which is required by the regulations, would be met.
The RCD would not necessarily disconnect in 0.2s under all circumstances but this is not required at all by the regulations.
 
If anyone is going to base whether an installation is safe according to the regs at the time of the installation, they would need to know the date of installation, how often are we blessed with this information? Once upon a time fused neutrals were considered a good idea. Its really up to the individual at the time to make an educated assessment of coding required, many amendments are for the better, some have taken a backward step IMHO. I like to base my decisions on worse case scenarios, can't go far wrong then.

If you were experienced, you would/should be able date an installation to a regulations edition, with some accuracy. Unlike today, Regulations didn't change at anywhere near the regularity they do today... Unfortunately we have 17 day whizz kids and electrical trainee's undertaking/conducting EICR's that haven't got a clue what they are looking at, let alone being remotely able to make an educated assessment. Depends on what you mean by ''worst case'', ..if that means assessing a totally improbable scenario, as being possible, what is that saying?? lol!!
 
So what was actually wrong with the long standing previous 0.4 second disconnection times?? Which i might add, is still the disconnection time value for many countries around the world, as well as TN ADS systems in the UK!!
 
No matter how experienced one is, you could never always prove that an installation was installed as per requirements at the time.
I've been in this game 42 years this coming June , and I'm still blimim learning!
I like to try and keep up to date, and have many reference books at my side, its great to know they will all be out of date again come next January. You are certainly right about regs not changing like they do today.
 
So what was actually wrong with the long standing previous 0.4 second disconnection times?? Which i might add, is still the disconnection time value for many countries around the world, as well as TN ADS systems in the UK!!

I never said anything was wrong with them, just that where an RCD is used for fault protection on a TT system the maximim permitted disconnection time is now 0.2s. Higher than this is considered unsafe by BS7671:2008
 
No matter how experienced one is, you could never always prove that an installation was installed as per requirements at the time.
I've been in this game 42 years this coming June , and I'm still blimim learning!
I like to try and keep up to date, and have many reference books at my side, its great to know they will all be out of date again come next January. You are certainly right about regs not changing like they do today.

Then you should have no problem dating an installation to a reg's edition. lol!! I didn't say you shouldn't test, ....testing is the only way you are going to be sure of any findings you make. Now come on, after 42 years in the game, do you really NEED all those installation by numbers OSG's etc??
 
I never said anything was wrong with them, just that where an RCD is used for fault protection on a TT system the maximim permitted disconnection time is now 0.2s. Higher than this is considered unsafe by BS7671:2008


Do you get ''deaded'' faster with a TT installation than a TN one then?? Or is it more about ensuring that RCD protection is included into all TT installations to prop up their 200 ohm Ra value?? lol!!:wings: Don't take this post too seriously now will you!! lol!!
 
Do you get ''deaded'' faster with a TT installation than a TN one then?? Or is it more about ensuring that RCD protection is included into all TT installations to prop up their 200 ohm Ra value?? lol!!:wings: Don't take this post too seriously now will you!! lol!!

Haha, no of course not, but when the current regulations deem something unsafe, then I will code it appropriately.
 
Then you should have no problem dating an installation to a reg's edition. lol!! I didn't say you shouldn't test, ....testing is the only way you are going to be sure of any findings you make. Now come on, after 42 years in the game, do you really NEED all those installation by numbers OSG's etc??

I'm afraid I do.
Once upon a time, I could quote regs numbers, but i seemed to have developed a type of dyslexia to all those numbers now lol. Too many regs referring to other regs for my liking.
When I update with a 17th edition course, I thought I was boy wonder again, but its all gone to mush again since :-(
I reckon I could still kick some arse installing MICC, making trunking sets that have near enough been banned, and bashing in some conduit with some intricate bends, but having spent most of my career on that side of the industry, I am almost enjoying catching up on the other side of things, and apart from my reference books, find many posts here enlightening.

I do believe when I attended college all those years ago insulation resistance and ring continuity with a wind up megger was about the most testing that happened. It could just be my memory though.
 
Part of the difficulty of dating an installation accurately (unless it is untouched and pristine), is that it is often a mish mash of different editions, for example it may have been originally installed to say the 12th then re-wired to the 15th, then at some point had the CU updated to the 16th etc..etc.

We can only really have an educated guess, unless there is prior paperwork (lol in domestic).

Where I disagree with Damien is that I would not fail a fully compliant 16th ed install, it is when you start going further back is where more and more problems arise, and the recommendations become more C2 than C3

The 0.4 disconnection time in the 16th was only for S/Os or final circuits which supply portable equipment and handheld class 1 equipment, for other fixed final circuits a disconnection time of not more than 5 seconds was permitted.

In my view the 16th edition is adequately safe, with no more than a C3 in respect to coding, going any further back and you start attracting C2s.
 
I'm afraid I do.
Once upon a time, I could quote regs numbers, but i seemed to have developed a type of dyslexia to all those numbers now lol. Too many regs referring to other regs for my liking.
When I update with a 17th edition course, I thought I was boy wonder again, but its all gone to mush again since :-(
I reckon I could still kick some arse installing MICC, making trunking sets that have near enough been banned, and bashing in some conduit with some intricate bends, but having spent most of my career on that side of the industry, I am almost enjoying catching up on the other side of things, and apart from my reference books, find many posts here enlightening.

I do believe when I attended college all those years ago insulation resistance and ring continuity with a wind up megger was about the most testing that happened. It could just be my memory though.

Much of the work i was doing during my training days (industrial manufacturing sector) and after, was testing!! Everything from ELV to MV installations, to systems control, using test equipment that went way way beyond IR and continuity tests.

Like you, i couldn't quote or spurt off Reg numbers, only really ever look at them, if i want a confirmation, or looking at another aspect of what can be done... I know what you mean about memory though!! lol!!
 
Part of the difficulty of dating an installation accurately (unless it is untouched and pristine), is that it is often a mish mash of different editions, for example it may have been originally installed to say the 12th then re-wired to the 15th, then at some point had the CU updated to the 16th etc..etc.

That the bit I was trying to convey, but you have explained it better than I.
 
These debates are good as it allows a good exchange of idea/onfo on a topic! I've often questions what the "tecnicalities" of the PIR process is so the thread has made me re-think my position so I thought I'd add my summized interpretation/view to continue the debate on PIR generally .....

Only guidance BS7671 (17th edn) gives on PIR is that it is conducted to determine :

1) If the installation is 'satisfactory' for continued use (note 'safe' not used )
2) That the requirements for disconnection times set out in BS7671(17th edn) are complied with
3) That departures from these regs BS7671 (17th edn) that may give rise to danger are identified.
4) On completion of the PIR an EICR shall be given to ..... showing any non-compliances to BS7671 (17th edn) that may give rise to danger.

And of course we have the caveat at the beginning of BS7671 (17th edn) that states previous installations may not conform with the requirements of BS7671 (17th edn) but that does not mean they are unsafe for continued use (note 'satisfactory' not used)

BS7671 (17th edn) offers an EICR model form along with guidance on codes to be use for observations raised within the EICR :
C1 -- Danger present (defined as risk of injury to persons/livestock)
C2 -- Potentially dangerous
C3 -- Improvement recommended
[Note : 'Observations' is not defined within BS7671 (17th edn) ]

In support of BS7671 (17th edn) we have documentation issued by the ESC on EICR's which is supported by all the major players in the industry (ECA, NICEIC etc ... ) and of course by the IET who 'own' BS7671 (17th edn). The key points it raises are:

1) The EICR provides an assessment against the requirements of the edition of BS7671 current at the time of the inspection, irrespective of the age of the installation.
2) It describes 'observations' as something which would contribute to a significant improvement in safety of the electrical installation and can be supported by one or more regulations in the edition of BS7671 being current at the time. Observations based solely on personal preference or 'custom and practise' should not be included.
3) The guide then advises that it is entirely a matter for the 'competent' person to decide on the classification code to use but gives specific example of where it believes a code should be applied.

My interpretation of the above means that I conduct EICR's using the model form in BS7671 and do it against the current edition of BS767 (17th edn) and any non-conformance to the 17th edn regulations I record as an observation. My view if is that if it wasnt a safety improvement on previous regs it wouldn't have been updated in the 17th edn. I then code that observation using the ESC guidance. If not covered in there then based on my 'experience' I decide if I consider it dangerous or not.

Bottom line is I believe my 'butt' is covered by following BS7671 (17th edn) and the ESC guidance should there questions/prosecution arising from my PIR. But as a 'competant' inspector there is nothing stopping anyone not following any guidance and conducting a PIR as they see fit and then reporting the results of that inspection in any form they want to ---- until something goes wrong and they are asked for justification. Or more importantly perhaps under the EAWR proving innocence rather than the prosecution having to prove guilt!

In the example contained within this thread Im in agreement with Mr Skelton -- if it doesnt meet disconnection times C2. I'm just reporting my findings to the customer against the current BS7671 and its upto him if he wants to ignore them or do something about them. I can't make him do anything if he doesn't want to.
 
That all fine, but giving a fail code to a circuit or whatever, that has proved to have been adequately suitable (fit for purpose) and in working order and hasn't been changed a jot, since installed. The only change being made being a disconnection time change. I think you would need to be able to substantiate giving that situation a fail code!! Code 3 is fine!!

I'm yet to be convinced, that a 0.2 difference in disconnection times is going to make much if any difference in a situation where RCD's are basically mandatory (TT systems) for compliance with earth fault disconnection times!!!
 
Badged01, I am on the fence on this one all be it leaning slightly towards Damian and your self's view , after this post .
Good argument well put IMO !



Edit ; I say on the fence , but have always gone with a C3 until now .
 
One last question for those that would C2 a compliant 16th edition install. lol

How are you going to code existing 17th installs once 17th amd3 becomes the new standard with reduced max Zs's and all that this implies ?

Edit: Badged I gave you a like for your very good post, but I don't agree with you wrt 16th, the regs are not retrospective as such, and to fail an immediately previous edition is harsh IMO, I would still C3 it, and make a note that it complied with that previous edition, ie. recommend improvement.

If it was earlier, say 15th with a VOELCB, which are now classed as an ineffective protective measure, then yes a C2 is appropriate.
 
Last edited:
Ultimately its down to the inspector if he wants C2 or C3. For me the key question you have to answer is if it doesn't comply with the latest 17th edn regs for a new build would you accept it as being satisfactory and sign off the new build paperwork (the installation is safe to go)? If you wouldn't sign it off why not (old installations to 16th edn meet those disconnection times)? If you wouldn't sign it off for those reasons why do you consider an old installation disconnection times acceptable on an EICR?

Code C2 or C3 is a judgement call, mine is a C2 - potentially dangerous. If the old disconnection times were acceptable why did we change them? In reality you can give either as the only time you would need to justify the code would be should an 'accident' happen and my butt is covered :)

And yes, there will be further issues with installations now designed to specific disconnection time in the 17th edn which may not now comply with new times in the BYB!! At what point do you draw the line in the sand and say any disconnection time from the XXth edition is acceptable ......
 

Reply to TT eicr code? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

See this time after time - poor installation: new split load board on a re-wire tt installation. The main switch is not a time delay rcd. The...
Replies
2
Views
321
Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Replies
4
Views
2K
So I'm getting various responses to this depending on how things are interpreted. Here's a scenario: Assume property is a tenanted property...
Replies
25
Views
2K
Afternoon all, Just wondering what everyone's response to the following scenario is. Letting agents have asked us to carry out an EICR. There was...
Replies
42
Views
5K
Did a couple of inspections on 2 x 2 bed ground floor flood damaged flats today, only 4 circuits in each, bizarrely one socket circuit and 2...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock