Search for tools and product advice,

Discuss TT High Zs in the UK Electrical Forum area at ElectriciansForums.net

P

paulk11

Evening. Did a Zs test today on a TT lighting circuit and got a reading of 335ohms. I haven't checked Ze yet but I'm presuming that's also in the same ball park. I'm aware of the upper limit Zs of 1667 and the advice contained within the good book that states Zs should be below 200, so I'm in the middle. I've advised homeowner that it should be reduced if possible and I see a couple of options; Add an earth rod or increase the main earth with a 16mm CSA cable (it's currently only 6mm). It's been pouring with rain all week so no point adding water. Any other suggestions? Thanks
 
Changing the CSA of the cable to the stake isn't going to help that much with a RA that high... best add a 2nd and possibly a 3rd rod, and make sure they go nice and deep!
Where do we stand regarding the 200ohm limit though? If max is 1667 then why worry at all?
 
It is considered unstable above 200ohms
 
Changing the cable from 6 to 16mm will only make a tiny difference, less than 1 ohm for sure.
Although the high Ze is strictly speaking acceptable combined with 30ma RCD protection I'd try and get it lower.
A decent 5/8 rod even 2 coupled together should make a difference although I know how hard it can be to get a rod in the ground in many places 'down west' in Cornwall. :)
 
Yes
It is considered unstable above 200ohms
Yes, I got that bit as its stated in 7671 but can someone elaborate on the 'unstable' bit. What does that actually mean? Why should we worry as the max permitted is much higher? Trying to comprehend it (still). Cheers
 
Changing the cable from 6 to 16mm will only make a tiny difference, less than 1 ohm for sure.
Although the high Ze is strictly speaking acceptable combined with 30ma RCD protection I'd try and get it lower.
A decent 5/8 rod even 2 coupled together should make a difference although I know how hard it can be to get a rod in the ground in many places 'down west' in Cornwall. :)
It's on an estate so may be doable
 
The max 1667 ohms applies if the breaker controlling the circuit is 30mA. I would suggest a ze test carried out and a reading of sub <200 ohms should be obtained for a stable earth reading.
 
If it is on an estate probably isn't using the rod as a return anyway. Be interesting to know the Ze with the bonds isolated, could be a case of the earthing conductor doing no more than earthing the electrode.
 
If it is on an estate probably isn't using the rod as a return anyway. Be interesting to know the Ze with the bonds isolated, could be a case of the earthing conductor doing no more than earthing the electrode.
When I say estate, I mean that in the loosest possible terms!! There's a few houses, big for these parts!!. Ze (or Ra on a TT) is the next move and then perhaps an extra rod. May call dno too to enquire. Thanks very much.
 
Yes

Yes, I got that bit as its stated in 7671 but can someone elaborate on the 'unstable' bit. What does that actually mean? Why should we worry as the max permitted is much higher? Trying to comprehend it (still). Cheers

The fact is that Bs7671 does not give a maximum Ra value and does not state that the value must be stable....only that a value exceeding 200 ohms may be unstable. Nobody has ever given a valid reason as to why it needs to be stable as far as I can recall.
People pluck values out of the air for their preferred maximum..The NIC seem to favour 100ohms,and I recall a poster on here saying he gets twitchy if it's over 80 ohms. Nobody has ever given a valid reason for their preferred value.
If your Ra is around 335ohms then it is in full compliance with Bs7671 and you need do no more, although you may choose to .
In that case pluck a figure out of the air like everyone else seems to do.
 
Mind you 335 at the moment when it's rained heavily for ages and the ground is pretty saturated could go sky high when the ground dries out.
 
Mind you 335 at the moment when it's rained heavily for ages and the ground is pretty saturated could go sky high when the ground dries out.

Probably not by around 1300 ohms though!
This is where it gets silly because of 7671's vague requirements, it's left to the tester/installer to decide what is acceptable...10...20...80...100...200 ohms? Whatever you fancy.
 
Mind you 335 at the moment when it's rained heavily for ages and the ground is pretty saturated could go sky high when the ground dries out.
Yes - my thinking too. I haven't checked the 'above 200 unstable' statement in Table 41.5 but I'm prepared to accept it.

For a really good debate - what code would you give this, if any? :)
 
I've read here, that depending on how you carry out your Zs test, you might not be getting an accurate figure. Try bypassing RCD and two wire high current test. See what result you get then? Do Ze test, R1+R2 test?
 
The fact is that Bs7671 does not give a maximum Ra value and does not state that the value must be stable....only that a value exceeding 200 ohms may be unstable. Nobody has ever given a valid reason as to why it needs to be stable as far as I can recall.
People pluck values out of the air for their preferred maximum..The NIC seem to favour 100ohms,and I recall a poster on here saying he gets twitchy if it's over 80 ohms. Nobody has ever given a valid reason for their preferred value.
If your Ra is around 335ohms then it is in full compliance with Bs7671 and you need do no more, although you may choose to .
In that case pluck a figure out of the air like everyone else seems to do.
Ha ha! That seems to sum it up nicely Wirepuller! I'll have to discuss with the customer and see what she wants to do but an extra earth rod is looking likely. Cheers
 
Yes

Yes, I got that bit as its stated in 7671 but can someone elaborate on the 'unstable' bit. What does that actually mean? Why should we worry as the max permitted is much higher? Trying to comprehend it (still). Cheers

BS7671 only states that values above 200 ohms may be unstable, it is not a definitive figure or a target value.
You should aim to achieve a value of Ra as low as possible, ideally low enough for ADS.
Instability is often a result of seasonal changes in ground conditions, especially cold weather causing freezing of the ground. A number of deep driven earth electrodes in parallel will provide a far more stable value than a skinny 4' rod.
I usually start with 2x 8' long 5/8" dia rods spaced as far apart as possible for a small installation and take it from there.

If soil conditions prevent driving the rods to a sensible depth then other options need to be explored such as horizontal electrodes.
 
The fact is that Bs7671 does not give a maximum Ra value and does not state that the value must be stable....only that a value exceeding 200 ohms may be unstable. Nobody has ever given a valid reason as to why it needs to be stable as far as I can recall.
People pluck values out of the air for their preferred maximum..The NIC seem to favour 100ohms,and I recall a poster on here saying he gets twitchy if it's over 80 ohms. Nobody has ever given a valid reason for their preferred value.
If your Ra is around 335ohms then it is in full compliance with Bs7671 and you need do no more, although you may choose to .
In that case pluck a figure out of the air like everyone else seems to do.

It needs to be stable as an unstable value will change and could exceed the maximum permitted value with seasonal variations in ground conditions.

Stability is not just about getting a low Ra, a high Ra from a well designed earth electrode will be more stable than a low Ra from a single short rod.
 
It needs to be stable as an unstable value will change and could exceed the maximum permitted value with seasonal variations in ground conditions.

Stability is not just about getting a low Ra, a high Ra from a well designed earth electrode will be more stable than a low Ra from a single short rod.

Good reason for stability, (perhaps)!.....but the 'over 200 ohms may be unstable' guidance is clearly a joke as stability has nothing to do with the ohms value of the electrode. The OP's 335ohms may well be more stable than another rod with a 50ohm value.
 
I've read here, that depending on how you carry out your Zs test, you might not be getting an accurate figure. Try bypassing RCD and two wire high current test. See what result you get then? Do Ze test, R1+R2 test?
The OP hasn't actually tested the earth rod or got a Ze figure yet.

So perhaps we should wait for that before we start hammering in new earth rods etc ;)
 
I had an argument with a NIEIC assessor over this very subject. During an assessment a good few years back one of the installations was a TT.
The Ze measured at the time was 107 ohms, the assessor questioned this value.

I responded by stating that in the regs a value of less than 200 ohms was considered stable and acceptable. He refused this and said that the NICEIC would not accept a value greater than 100 ohms.

I was unaware of this at the time and asked for a valid explanation for the reasoning behind this? He had no definitive answer and just kept repeating that it was just not acceptable by the NICEIC. I argued that it was by the regs guidelines and therefore was no problem. Anyhow he got the hump and failed my assessment based on the fact that I had not complied with the NICEIC standards. I phoned the NICEIC office explained what had transpired and complained about my failed assessment. They couldn't explain to me why the value of 100 ohms was the acceptable one set by them. They just quashed the failure and re-instated my compliance with no other action or assessment required.
 
Yes - my thinking too. I haven't checked the 'above 200 unstable' statement in Table 41.5 but I'm prepared to accept it.

For a really good debate - what code would you give this, if any? :)

I'd seriously consider a C3 if part of an EICR or maybe no code and a comment, I do like to see a value well under 200 ohms ideally.
 
Do you need to?

My understanding of C3 is that the item does not comply with Bs7671 but is not considered to compromise the safety of the install. So a C3 cannot be applied if it complies with Bs7671.
Some might argue that as 200ohms is mentioned then that is effectively a regulation, however a maximum Zs of 1667 ohms would seem to contradict that.
TBH though it's a bit academic either way....a C3 will not stop a satisfactory EICR so it hardly matters really.
 
542.2.4
The type and depth of an earth electrode shall be such that soil drying and freezing will not increase its resistance above the required value

Just food for thought,if everybody were to comply with the above regulation,the questions about stability would not be relevant :)

Now,If the value were low enough to operate the Rcd (be it a 30,100,300 or 500) and that value was typical of the conditions found in the area, the Ra could be almost any figure below the operating value as long as it does indeed operate the device

My conclusion would be the maximum resistance of the earth electrode can be almost anything you want it to be, as long as the above reg is satisfied,the 100 ohms or 200 ohms or even higher may be figures that may be of little practical benefit :clapping:
 
542.2.4
The type and depth of an earth electrode shall be such that soil drying and freezing will not increase its resistance above the required value

Just food for thought,if everybody were to comply with the above regulation,the questions about stability would not be relevant :)

Now,If the value were low enough to operate the Rcd (be it a 30,100,300 or 500) and that value was typical of the conditions found in the area, the Ra could be almost any figure below the operating value as long as it does indeed operate the device

My conclusion would be the maximum resistance of the earth electrode can be almost anything you want it to be, as long as the above reg is satisfied,the 100 ohms or 200 ohms or even higher may be figures that may be of little practical benefit :clapping:

Good points....I wonder how compliance with that regulation could be verified on an EICR? It would be very difficult to gauge the depth of an electrode without digging it up!
 
Good points....I wonder how compliance with that regulation could be verified on an EICR? It would be very difficult to gauge the depth of an electrode without digging it up!

Simple, it's exactly the same as checking any other test results on an eicr. Measure the value and compare it to the previous test results, then you can assess any change which may have occurred.
After all one of the fundamentals purposes of carrying out tests and recording the results is to identify changes and trends in changes of the results in order to predict and prevent failures and identify maintainence requirements.
 
If the value of the Ze is above the 200 ohms set by the guidelines but below the maximum permitted value of 1667,ensuring additional protection is correctly installed and operational (RCD) and thus compliant, the installation is perfectly safe to use.

I think a C3 would be reasonable code to note on the EICR. As a value greater than 200 would in theory require further investigation to ascertain stability.

One way to achieve this would be to test the Ze over a period of time under different environmental conditions and then compare the results. I doubt any of us would be in a position to do such monitoring, let alone the cost of such.
So one simple less costly solution would be to install additional rods... to try and achieve a value much less than 200 ohms.
 

Reply to TT High Zs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
624
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock