Darren80

DIY
Reaction score
0
Hi I have a property and the mains supply is a TT system I need to put a temporary static caravan in the garden. The caravan will have a water supply to it and the cooker is gas. The caravan has its own CU rated at 40A with a 32A RCD. The distance is about 100m. My question is do I need a earth rod at the van and if so do I need to keep the earth in the SWA separate like you do in a PME system or can they be connected together.
Thanks
Darren
 
If it is a new circuit in England & Wales that is notifiable work, so getting a professional in is the best answer in many ways. There may be folk on this forum in your area who can do a good job.

You also need to identify the actually demands of the caravan - not just the 40A rating of the caravan CU, as that will have a big impact on the design in terms of cable size and hence cost to keep the voltage drop within the regulations.

As for earth rods on TT there is no harm in having another rod at the caravan as lower impedance is generally safer, though as the main property is TT you should not need it as the cable's armour will generally be adequate and should be reliable if properly glanded at both ends. Whoever does the job ought to check the supply characteristics first in any case.

Also note that caravans must have double-pole 30mA RCD protection, and obviously waterproof connectors. Normally you get outdoor rate socket/RCD outlets to allow them to be plugged in using something like a 16A or 32A commando style plug (assuming your max load is 16A or 32A of course). So your circuit would be SWA to the socket outlet next to the caravan (as you specify it as 'temporary' and so not hard-wired).
 
Last edited:

Reply to TT supply to a static caravan in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
899
Had a call from a local caravan site… under new ownership, and creating some new pitches. Went to site to have a chat, the guy already knew I’ve...
Replies
9
Views
2K
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
690
We have started a business building garden rooms/caravans/mobile homes under the caravan act. We have only done one so far and I got an...
Replies
3
Views
1K
I am an apprentice and was just wondering the reason why you have to put a separate earth into a caravan? My friend has asked me to do a hobble...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock