Discuss Twin and Earth riser - buried in the wall. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
55
Putting a new CU into a flat. The riser is protected by a fused switch (immediately after the meter). The riser is in 16mm T+E i.e non armoured. I can't see it anywhere so it must be within the fabric of the building Is this a non compliance?
 
If the cable is < 50 mm from surface then it requires additional protection in the form of
A 30mA rcd
B cable has sufficient mechanical protection covering it (3mm plate steel)
C cable is installed in earthed metal containment (conduit or trunking)
D cable has an earthed metal covering such as swa which can withstand fault currents from being Penitrated by nails and screws.

If cable is buried in a wall with metal parts other than screws then depth is irrelevant and cable must be protected by options A-D

As the cable is exiting to cu and it would cause major disruption to do either of the options then I would personally just make a remark on the test certificate

As has already been covered by the other lads posts bonding is something that needs considering as already said the cpc in 16mm will be 6mm.
Only really acceptable if it's a TN-S system or TT.
 
As Tel says - it's normally a 6mm cpc on 16mm T&E and may not be sufficient for an earthing conductor.
A 6mm may be satisfactory as a cpc provided the Adiabatic equation is satisfied, however if you mean as a combined cpc/ bonding conductor then if pme it won't be.
 

Reply to Twin and Earth riser - buried in the wall. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
827
Hi, The current carrying capacity tables in the BS 7671 for twin and earth cables are only for buildings that have thermal insulation. I'm...
Replies
48
Views
4K
I've been told I need to upgrade the main earth bonding to 16mm. The consumer unit is on the wall adjacent to the externally mounted incoming...
Replies
30
Views
4K
Apologies if this is in the wrong section - appreciate it's more of an educational question. That said I have 2391 - but the classroom environment...
Replies
2
Views
2K
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock