Discuss Two PIR sensors to work same lights in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi all

Does anyone know of PIR sensors that can be connected to switch on the same lights.
Basically, i need to install 2 sensors located around the corner from each other and either of these two sensors need to switch on 4 led wall lights.
Spoke to Knightsbridge, they say that this can't be done as you would be sending a switched live back down to the other sensor that hasn't activated.

Has anyone installed PIR's like this without any issues? If so, what ones have you installed?

Thanks for any input.
 
I have done exactly the above with the standalone sensors from screwfix and they have been working fine for around 4 years now. They switch approx 10 x LED's going up a pathway.
lights.jpg
 
Hi all

Does anyone know of PIR sensors that can be connected to switch on the same lights.
Basically, i need to install 2 sensors located around the corner from each other and either of these two sensors need to switch on 4 led wall lights.
Spoke to Knightsbridge, they say that this can't be done as you would be sending a switched live back down to the other sensor that hasn't activated.

Has anyone installed PIR's like this without any issues? If so, what ones have you installed?

Thanks for any input.

As long as the total load of lights does not exceed the switched rating of one of the PIR'S then there is no problem in paralleling the outputs from them.
 
I have done exactly the above with the standalone sensors from screwfix and they have been working fine for around 4 years now. They switch approx 10 x LED's going up a pathway.
View attachment 48040

Hi HHH. Am I reading your drawing correct? It looks like your timer output is in parralel with your PIR outputs. Is that what you wanted? PIR operation with a timed override?
 
Hi HHH. Am I reading your drawing correct? It looks like your timer output is in parralel with your PIR outputs. Is that what you wanted? PIR operation with a timed override?
The customer wanted them to come on at a certain time in the evening and then switch off, but also wanted them to be constantly (at night) on a PIR from top of drive and bottom of drive.
 
I know Luxomat sensors are quite happy having power fed into the switched live output.

Depending on the area you are covering though, you can get corner sensors that look all around.
 
Nothing wrong with that unless Knightsbridge are suggesting the 'inrush current' maybe a problem and not because of sending a s/l back to the other sensor.
When they start 'playing up', (they invariably do!), you get the ladder up to investigate the sensor and it will always be the other one!
 

Reply to Two PIR sensors to work same lights in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I just found this forum last night and figured I would post my issue since I can't find much out there with a similar situation. My job...
Replies
4
Views
462
Hi, Heavy industrial spark here, never do house bashing hence the question. I currently have a light switch at the front door not doing anything...
Replies
1
Views
478
Hi All, I need a bit of advice. My client is asking for a rather silly lighting setup in his bathroom and I am struggling to understand...
Replies
3
Views
2K
Thinking a 240V AC relay activated by two independent light switches could be used to switch power to a shared inline extractor fan. The fan...
Replies
31
Views
2K
Can I use multiple GU10 led lamps with their own PIR sensors in the same room? I have a row of existing lamps 600mm apart in a straight line & I...
Replies
9
Views
842

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock