Discuss Type c RCBO in the Industrial Electricians' Talk area at ElectriciansForums.net

M

mick21

Hi all
I have recently obtained some type c RCBOs, can anyone tell me if these would be ok to use in a domestic consumer unit, they are wylex and MK. Not sure if they would fit.
Thanks in advance.
 
Interesting point here!

City & Guilds 2391-10 question:

List the possible methods of overcoming an exceeded maximum Zs on a circuit currently protected by a BS 60898 'B' 32 MCB
 
Interesting point here!

City & Guilds 2391-10 question:

List the possible methods of overcoming an exceeded maximum Zs on a circuit currently protected by a BS 60898 'B' 32 MCB

Increase the size of the CPC would be one and the other would be fit RCD/RCBO ......................so the zs if RCD/RCBO would be a 1667 as it would have to be a 30mA ......................correct sir? ;)
 
Increase the size of the CPC would be one and the other would be fit RCD/RCBO ......................so the zs if RCD/RCBO would be a 1667 as it would have to be a 30mA ......................correct sir? ;)
or reduce the rating of the breaker ( if load will allow).
 
Yes, supplementary bonding, increased CSA of CPC, RCD protection incorporated, reduce In of the MCB or reduce the type eg. 'D' to 'B' if the load characteristics allow. (not applicable in this situation as the question relates to a 'B' type.)
 

Reply to Type c RCBO in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

I am upgrading garage lighting. I have installed 12 40W batten lights (cheap Amazon variety - don’t have specs). 6A breaker in Garage consumer...
Replies
16
Views
3K
Hi, I recently had an EICR done at my property which unfortunately was unsatisfactory. So the electrican advised a new fuseboard from BG General...
Replies
90
Views
3K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
732
Hello all.. I'm quoting for some work and would like change the type AC RCBO to a type A. Consumer unit is a castlec which I have not come...
Replies
5
Views
918
Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
898

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock