Discuss types of earthing to be carried out for 3 phase standby generator which is separately driven system in the Commercial Electrical Advice area at ElectriciansForums.net

Reaction score
3
3 phase standby generator of rating 30KVA is to be install in the lightning prone area. The utility main line is TT arrangement where neutral point is grounded with 3 phase and neutral wire provided to load system.
A separately driven generator ( standby generator) is also needd with TT earthing arrangement .Do i need to ground the neutral coming out he alternator provided that metallic frames of generator is earthed to separated grounding system ( neutral and body are not bonded)
will you please provide the complete detail regarding the installation of generator with earthing arrangement and value of earth resistance require for the earthing system both for neutral grounding and body earthing
 
The output of a generator would normally be TNS not TT, the star point would be connected to earth electrode and to the generator frame.
The earth electrode should have as low a resistance to earth as is possible.
 

Reply to types of earthing to be carried out for 3 phase standby generator which is separately driven system in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
533
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
965
Hi guys I was recently ask by a customer if/how his house could be supplied by his electric car. He wants to charge the car at night on low rate...
Replies
4
Views
1K
Hi everyone, I live well off grid in Wales and am presently renovating a small property. As part of that renovation I have had a full off grid...
Replies
13
Views
11K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock