Discuss UFH T&E Cable Melting / Heat Damage in the UK Electrical Forum area at ElectriciansForums.net

Andrew9

EF
Reaction score
3
I was tracing some electrical cabling last night and noticed a ~6" section of 2.5 T&E cable that appears to have been subject to heat damage and the plastic has started to melt. It's about 1m away from the CU in the garage and connected to a 32amp MCB. It's a radial circuit that powers a small 4 sqm section of UFH int the utility room. I have no info on UFH as it was installed before we bought the house. Luckily we never really used it.

So from what I can see the circuit looks something like this:

32 Amp MCB (Contactum B Type) --> Damaged section of cable --> Switched fuse on garage wall --> into wall cavity --> Once it goes into the wall cavity i have no idea where it goes.

Needless to say, I've isolated the circuit at the breaker and won't be turning back on until an electrician has advised and fixed. There's a second identical circuit that provides power to the UFH in the kitchen. I've also isolated this despite there being no visible damage.

I'm interested to see what you guys think the problem is. Did the MCB fail or is 2.5 T&E no suitable for a 32amp circuit? Do you think there's a fault with the UFH or maybe just a faulty run of cable?

One good outcome from all this is that it's made me realise i need a fire alarm and CO2 extinguisher in the garage.


Capture.JPG
Capture3.JPG
 
I would say that damage is actually caused by a plumbers blow torch.

With the PVC turning white like that, it's been exposed to a very hot heat for a short period of time.

The cable has been burned from the outside.

Edit:

A 32amp MCB isn't ideal for the situation. However not against the rules as it is a fixed load. Providing it meet other circuit tests that should have been completed on installation. I can't see UFH being anything other than a resistive load, so little to no inrush when powering up.
 
Is it possible that the plumber did it with his blow lamp? It's very close to the soldered joints, and the damage appears to be at the bottom edge only.

If not then it's very very localised, and could possibly be e a cable fault.
[automerge]1566987498[/automerge]
Rob got there before me. Only by seconds though - I'll get there next time!
 
agree with both above posts. deffo the wet-pants has been let loose within a mile of the cables. recipe for disaster. having said that, a 2.5mm radial circuit should be protected by a MCB <25A.25A MCB is not common, so a 20A or a 16A is usual. 4sq.m of ufh is generally < 1kW, so even a 10A would suffice.
 
I think you're both right. Hadn't even considered that. I had a new boiler fitted over the winter and the plumber needed to replace the existing pipe work with a wider diameter pipe. What an idiot. He'd have definitely noticed that but chose not to say anything. I couldn't stop him banging on about the importance of Gas regulation and health and safety.

So I guess the good news is i just need to replace the stretch of damaged cable.

Thanks guys
 
You would have thought he'd have put a heatshield over the cables. And yes, he would have noticed the damage and not said anything - very disappointing. I'd show him the damage to be honest - you should at least ask for your first boiler service to be done FOC.
 
plumbers have limited vision. they can't see anything apart from their pipes and the fact that sh!t flows downhill.
[automerge]1566989160[/automerge]
tell the wet-pants to invest in 1 of these:
1566989163584.png
 
Last edited:
You would have thought he'd have put a heatshield over the cables. And yes, he would have noticed the damage and not said anything - very disappointing. I'd show him the damage to be honest - you should at least ask for your first boiler service to be done FOC.
No way he's coming back. I'll just make sure the local community know what he's capable of.
 
plumbers have limited vision. they can't see anything apart from their pipes and the fact that sh!t flows downhill.
[automerge]1566989160[/automerge]
tell the wet-pants to invest in 1 of these:
View attachment 51706

Don't they have some heat proof material for instances like this. (You know what I mean... :tearsofjoy:) Some think that protects the surrounding area...
 

Reply to UFH T&E Cable Melting / Heat Damage in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi all, Have a relatively simple question. Doing a rewire to make a circuit in a single room. My father is a retired spark, so no worries about a...
Replies
7
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
I have a question,about cable loadings, just to satisfy my own curiousity. The background detail is a bit long, apologies. If you get bored...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock