Discuss (UK) What's wrong with my lighting circuit? in the Lighting Forum area at ElectriciansForums.net

Reaction score
0
Hello all,
I recently redecorated my living room which meant stripping off the wallpaper. While doing so, some moisture got into the living room light switch (it's a 2-way). I took off the switch plate to dry it out but noticed a wire seemed to be unconnected. I'm assuming this black wire slipped out while I manipulated the switch around. I dried out the wiring and connected the loose wire to the black wires in the terminal block but there is now a problem with the rest of the circuit and I am not confident leaving it the way it is. Basically, what happens is that the 2-way switch works perfectly as before, but all the upstairs lights will not work unless this living room light is on. I am assuming the fuse box (old plug in style) runs to the kitchen, then the first of the 2-ways in the living room, then to the switch in question. After that, I think the loop must run upstairs. All the downstairs lights are fine, it's just the upstairs lights that will not work unless the living room light is on. It doesn't matter if the kitchen light is on or off, only the living room light. My understanding is that the lighting circuit is a sort of daisy chain, so it would appear there is a problem between the last downstairs point in the loop and the first upstairs point?
Any advice would be most welcome, thank you!
Mike
 

Attachments

  • WP_20191222_22_29_53_Pro.jpg
    73.3 KB · Views: 66
  • WP_20191222_22_29_13_Pro.jpg
    85.3 KB · Views: 64
Perhaps the black wire you connected into the chock block connector should be instead connected somewhere else? Just because it is black does not mean it is a N, nowadays it would have brown (or red) sleeving to indicate being used as a L, but often that was not done.

It looks like you've moved what is the feed to upstairs from being connected to permanent live, to lounge switched live. Moving one of the black wires will likely fix it, and hopefully you can remember which of the 3 black wires it was!
 
Hi - ah now you‘ve a first hand demonstration of the power of taking a pic of the existing wiring. I still do this myself as it can save time at the end of the day :) .

It does sound like the permanent L is no longer going upstairs. But if the downstairs lights can energise upstairs lights I’m thinking more than just one black conductor has moved.
 
The fact that all the lights work with the blacks connected together, suggests that none of them is a switched line otherwise either a light wouldn't work or the MCB would trip when a switch was turned on.

I think two red wires have been interchanged - the incoming PL and the SL to the living room light. Most likely, the red in the switch common is actually the incoming L and the three reds in the choc block are the far switch common, the living room light and the loop out.
 
I’m in Aberdeen tonight if you get stuck.
Just don’t swap too many cables about.

Hey there, so sorry I have been out all day and just seen this.
[automerge]1578353521[/automerge]
The fact that all the lights work with the blacks connected together, suggests that none of them is a switched line otherwise either a light wouldn't work or the MCB would trip when a switch was turned on.

I think two red wires have been interchanged - the incoming PL and the SL to the living room light. Most likely, the red in the switch common is actually the incoming L and the three reds in the choc block are the far switch common, the living room light and the loop out.

Thanks very much for the advice LN, I will check this out when I have the chance.
 
im in Aberdeen for a couple of days. brought my daughter up to uni, and her friends parents have bought a flat. Im putting in smoke detectors and a new consumer unit. gonna be a long day tomorrow
 
im in Aberdeen for a couple of days. brought my daughter up to uni, and her friends parents have bought a flat. Im putting in smoke detectors and a new consumer unit. gonna be a long day tomorrow

Hello again, thanks for getting back. Sounds like a busy day for you indeed.. I'm actually in Peterhead which is about an hour up the road, so a bit much to ask you to have a look, just while you're up here! Let me know if you've any free time and I will PM you.
 
sorry, mate... i'm not driving another hour... took me 4 to get here!
I think Lucian has it sussed,,, the reds have got mixed up so the switch is turning the whole upstairs on and off
 

Reply to (UK) What's wrong with my lighting circuit? in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
671
Hi, I’m new to the forum. Thanks for letting me join. Asking for some diy advicd… I’m trying to add a couple more security lights to the existing...
Replies
1
Views
632
Hello, I'm replacing standard light switches in my hall and landing with touch switches (not smart, just touch on/off) like these from Amazon...
Replies
7
Views
619
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
406
Hi, I’m looking to install 3 meross smart switches for 3 lights: entrance switch: only 1 gang but 3 way switch bedroom switch: 2 gang (1 is 1...
Replies
9
Views
362

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock