What implications are there from underspecifying an inverter?
(1) What actually results at the inverter, should the irradiance on the panels attempt to generate more than the peak rating of the inverter? (Design Volts are below max as are design amps) tripout? restart? smooth limit to max and continue uninterrupted?
(2) May be running near 100% for a longer period of time than usual - affect on reliability?
(3) Using eg SMA SB 3000TLs, can the max POWER be set in the software setup, or is this a CURRENT limit that is set this way? and (4) what range of setting is generally available (5%? or any%?)
(5) Because the total is over 16A/4kW, what additional specs do I have to meet and how do I achieve those specs?
I need to install a twin roof twin inverter (need to monitor each roof/direction separetely) system as follows:
3.12kW SSW plus 4.68kW NNE (ie. TIC = 7.80kW).
DNO has indicated that 5.96kW total max generation would be acceptable on this single phase domestic install at the installation address.
I intend to use a pair of SB3000TLs, each set to a max power of 2.98kW, say, to meet the DNO limit.
SSE roof of 3.12 will probably max at under 2.98 anyway, but the NNE roof of 4.68 looks severely underspec'd, until you consider the likely max irradiance around 70% of due south. So 0.7 * 4.68 giving 3.276kW.
Can this arrangement be safely and reliably achieved?
Thanks for looking,
Steve.
(1) What actually results at the inverter, should the irradiance on the panels attempt to generate more than the peak rating of the inverter? (Design Volts are below max as are design amps) tripout? restart? smooth limit to max and continue uninterrupted?
(2) May be running near 100% for a longer period of time than usual - affect on reliability?
(3) Using eg SMA SB 3000TLs, can the max POWER be set in the software setup, or is this a CURRENT limit that is set this way? and (4) what range of setting is generally available (5%? or any%?)
(5) Because the total is over 16A/4kW, what additional specs do I have to meet and how do I achieve those specs?
I need to install a twin roof twin inverter (need to monitor each roof/direction separetely) system as follows:
3.12kW SSW plus 4.68kW NNE (ie. TIC = 7.80kW).
DNO has indicated that 5.96kW total max generation would be acceptable on this single phase domestic install at the installation address.
I intend to use a pair of SB3000TLs, each set to a max power of 2.98kW, say, to meet the DNO limit.
SSE roof of 3.12 will probably max at under 2.98 anyway, but the NNE roof of 4.68 looks severely underspec'd, until you consider the likely max irradiance around 70% of due south. So 0.7 * 4.68 giving 3.276kW.
Can this arrangement be safely and reliably achieved?
Thanks for looking,
Steve.