Discuss ungrounded 3 phase systems in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
hello. looking for advice on working on a 3 ph, 3 wire 480 delta that i believe fits the definition of a corner grounded delta. the title of the thread is appropriate because theres only 3 wires marked for each phase and no neutral going into the customers main disconnect switch which powers a 3 phase 480v motor control circuit.
i say its corner grounded because there appears to be a bonding strap tying the middle phase conductor to the meter enclosure but am puzzled at why its bonded at that location especially when the manufacturer's label states specifically, "When service is not grounded, remove [this] bonding strap..."
i think the meter enclosure was intending for the middle conductor to be a neutral (a grounded system) but in this case its not (3 wire, 3 phase delta) or at least not supposed to given the customers requirements for a 3 ph 480v motor.
so my question is where is the proper place to ground a phase conductor? at the pole or pad mounted transformer? at the customer's first disconnect? or at the meter or anywhere else?

i will post pictures as soon as i can figure out how to do so.
 
adjusted the tint here to make the red label more legible which reads "When service is not grounded remove bonding strap re-install screw" bondingstrap_belowmeter (2).jpg

notice how its grounded here grnd screw_bonding strap (2).jpg
strap_frontmeter2.jpg
 
Last edited:
hello. looking for advice on working on a 3 ph, 3 wire 480 delta that i believe fits the definition of a corner grounded delta. the title of the thread is appropriate because theres only 3 wires marked for each phase and no neutral going into the customers main disconnect switch which powers a 3 phase 480v motor control circuit.
i say its corner grounded because there appears to be a bonding strap tying the middle phase conductor to the meter enclosure but am puzzled at why its bonded at that location especially when the manufacturer's label states specifically, "When service is not grounded, remove [this] bonding strap..."
i think the meter enclosure was intending for the middle conductor to be a neutral (a grounded system) but in this case its not (3 wire, 3 phase delta) or at least not supposed to given the customers requirements for a 3 ph 480v motor.
so my question is where is the proper place to ground a phase conductor? at the pole or pad mounted transformer? at the customer's first disconnect? or at the meter or anywhere else?

i will post pictures as soon as i can figure out how to do so.
All I can tell you that on a 3 phase delta system and the middle phase should be marked with orange tape meaning that the middle phase has much higher voltage. I’m not sure how you got a 3 phase delta service but I have never heard bonding the middle phase. Read with you meter on each phase to ground with the jumper wire removed and if I’m right you should read 120vac on phase A and C and phase B is going to be around 150vac
 
All I can tell you that on a 3 phase delta system and the middle phase should be marked with orange tape meaning that the middle phase has much higher voltage. I’m not sure how you got a 3 phase delta service but I have never heard bonding the middle phase. Read with you meter on each phase to ground with the jumper wire removed and if I’m right you should read 120vac on phase A and C and phase B is going to be around 150vac
its a 3 phase 3 wire system. line to line reads 480v across all 3 wires.
line to ground measurements is where it gets weird. A phase (labeled as x phase in the pic) to ground is 480v, C phase (labeled as z phase) to ground is also 480v. B phase (the middle phase in the pic) to ground is zero volts. you read that right. zero volts. that should tell any electrician worth his or her salt that that conductor is grounded. if you notice the ground wire is marked with white tape to signify it as a grounded conductor when its really the equipment grounding conductor since its attached directly to the pole ground outside the meter box. looking at all this i'm amazed the customer has had no electrical issues. judging by the size of the wires one can assume they don't draw a heavy load despite the 480v rating of the motors, but that's not my concern...

I believe B phase conductor needs to be marked as a grounded conductor to signify to any future electrician troubleshooting this service that it is such. I also have a problem with how its grounded-- that tiny ground screw is not meant for installing a ground wire. its there to ground the meter to the case as you can see in the pics. now there's a case ground lug located directly below and to the right of the meter (behind the red handle of the bypass lever). but proper equipment grounding isn't the real issue here. its how and why one of the phase conductors is grounded whether intentionally or not at that location.
 
All I can tell you that on a 3 phase delta system and the middle phase should be marked with orange tape meaning that the middle phase has much higher voltage. I’m not sure how you got a 3 phase delta service but I have never heard bonding the middle phase. Read with you meter on each phase to ground with the jumper wire removed and if I’m right you should read 120vac on phase A and C and phase B is going to be around 150vac
i forgot to mention that on a 4 wire, 3 phase delta if you read 120v phase to ground on any two lines then your third phase would actually read 208v. but yes that high leg should be marked as such on the customers main disconnect. i've seen quite a few of these 3 wire 3 phase ungrounded delta and they all read 490+ line to line, and roughly 240v-290v on any line to ground (voltage fluctuating because there's no neutral). on this service however you get a very solid 480v line to line and also to ground except B phase. its perfectly legal and safe (but not in this case i think) and is used for a very narrow application. i hear they are trying to move away from these ungrounded systems.

the bonding of the middle phase in this meter enclosure was intended, i believe, for a single phase 3 wire service where the middle conductor is the neutral. this actually applies to all standard single phase 3 wire residential services in the US-- with the neutral bonded at the meter socket (usually directly behind the meter in older homes with a 100 amp or less rated main)
 
i forgot to mention that on a 4 wire, 3 phase delta if you read 120v phase to ground on any two lines then your third phase would actually read 208v. but yes that high leg should be marked as such on the customers main disconnect. i've seen quite a few of these 3 wire 3 phase ungrounded delta and they all read 490+ line to line, and roughly 240v-290v on any line to ground (voltage fluctuating because there's no neutral). on this service however you get a very solid 480v line to line and also to ground except B phase. its perfectly legal and safe (but not in this case i think) and is used for a very narrow application. i hear they are trying to move away from these ungrounded systems.

the bonding of the middle phase in this meter enclosure was intended, i believe, for a single phase 3 wire service where the middle conductor is the neutral. this actually applies to all standard single phase 3 wire residential services in the US-- with the neutral bonded at the meter socket (usually directly behind the meter in older homes with a 100 amp or less rated main)
A true 480 volt 3 phase delta service should read phase to ground at 277 volt and phase to phase is 480 volts. I have never seen a 480 3 phase service run to a single family dwelling. How are you getting 120 for the receptacles and lights, 220 volt for dryer, stove, heat and air conditioning?
 

Reply to ungrounded 3 phase systems in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

BIG place OK lots of electrical bits. but one on a 3 phase Radial is tripping its RCCB so i check the wiring making sure its tight and it has...
Replies
5
Views
339
I have been asked if I can wire a motor for a car lifter in a domestic garage, however the motor is 3 phase and only single phase is available in...
Replies
5
Views
821
Good day to you. I need electrical drawings urgently and hopefully there is someone that can assist me. They are all for electrical trade test...
Replies
6
Views
798
Hi there, I built a house with ground source heating 5 years ago and it's a fairly large house so I have 3 phase supply 80 amps per phase. I had...
Replies
7
Views
957
Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock