Hi,
Ignoring the appauling conductor terminations which I found, in the background of the photo you can see a really odd neutral tail terminated into the main switch.

I've never seen this before, has anyone else, and if so what is it ? Oh I should add this is at a flat, so the tails are presumably coming from an central electrical cabinet. Flats were built in 2008.

It's part of an EICR, and I'm not even sure how to code it. Going to send it to Napit too, see what they think.20230928_114459.JPG
 
Last edited by a moderator:
Common in the UK as well. Used by DNOs for TN-S supplies, and its closely related cousin, concentric, is used for TNC-S supplies.
I've regularly used it for distribution to sub boards as well, but only where installation conditions don't require RCD protection.
 
I cant believe how short the stripped ends are. wow!!
 
Hi,
Ignoring the appauling conductor terminations which I found, in the background of the photo you can see a really odd neutral tail terminated into the main switch.

I've never seen this before, has anyone else, and if so what is it ? Oh I should add this is at a flat, so the tails are presumably coming from an central electrical cabinet. Flats were built in 2008.

It's part of an EICR, and I'm not even sure how to code it. Going to send it to Napit too, see what they think.View attachment 110835
I’ve seen this before where the installer hadn’t enough 25csa tail, so Connected multi singles to achieve the required result.

Very poor practice as, I’d always recommend sleeved Ferrules.
 
I’ve seen this before where the installer hadn’t enough 25csa tail, so Connected multi singles to achieve the required result.

Very poor practice as, I’d always recommend sleeved Ferrules.

What sort of ferrule would you recommend for the multiple cores of a split concentric cable?
 
Widely available in the UK.
It's not armoured, but it's extremely unlikely that a metallic object could penetrate it and make contact with the live conductor without shorting it to the neutral or earth .
The 'foil' is plastic, not metallic.
 
Widely available in the UK.
It's not armoured, but it's extremely unlikely that a metallic object could penetrate it and make contact with the live conductor without shorting it to the neutral or earth .
The 'foil' is plastic, not metallic.
Thanks for the reply. Can you please give me an example of where you’d consider using it. ???
 
I’ve seen this before where the installer hadn’t enough 25csa tail, so Connected multi singles to achieve the required result.

Very poor practice as, I’d always recommend sleeved Ferrules.
This isn’t multiple singles. This cable is made this way, so this isn’t bad practice. If you Google split concentric cable it’s a very common cable type, neutral and earth are multiple cores with live through middle as one core.
 
WOW, surely this is a DNO type requirement cable on a TT.????

No use for a TT supply as it has an earth in it.
Split concentric is used by DNO's for TN-S supplies but is also available for use in normal installations.
There’s NO armoured, and I take it that the silver wrap is flimsy foil.????
No there isn't an armour, but you wouldn't use it in a situation where an armour is required.
Obviously it can't be used for direct burial in an installation but is perfectly fine clipped direct, on cable tray, in risers etc.

This cable is widely used in blocks of flats for the BNO network, usually the orange LSF version of it.
 

Reply to Unusual Neutral Tail into Consumer Unit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I am due to carry out an electrical job in a third floor flat. Incoming supply is TN-S. Cannot locate a main earthing conductor inside the CU on...
Replies
4
Views
2K
Second post on an EICR I did today (always a good sign!) 70s flat with earthed conduit and singles. 6mm runs from the CU to presumably where an...
Replies
4
Views
2K
Afternoon all, I have been asked to change a consumer unit with a dual supply. I have a common supply, an off peak supply and one neutral, all...
Replies
11
Views
5K
Just carried out an EICR on a flat that was wired in the 70s - with singles run in earthed conduit to each point and the trunking providing the...
Replies
29
Views
4K
Background is we are selling our house and moving out of state. I've been fixing big and little things and painting for several months now, as...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock