Discuss Unusually low R1+R2 readings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
2
Hi All

So I've just extended two circuits and I've got home to type my results up for the certificate and I'm doubting my results, For the R1+R2 for the cooker circuit I got 0.02 ohms and for the ring I got 0.25 ohms, something seems a little off here.

Now by my calculations a 6mm cable should be giving me approx 0.03 per meter and the run to the board is approx 10m so i'm tinking my tester needs to go to be looked at, what do ya rekon?
 
Or you didn't null your leads
Or your machine is not quite as accurate as you like to think
Or there are parallel paths
Or your eyesight is getting like the rest of us and its those eyes that need calibration
icon7.png
 
Could be all of the above, I've just called the customer to tell them and that I'm sending my machine in to be recalibrated and then I'll be going round to retest, can't leave it with any doubt in my mind it'll drive me mad lol.
 
Is this 0.02 reading from your MFT's memory (if it's got one) or is it a transcription error?

No it wasn't from the MFT's memory, I wrote it down with the intention of typing it up when I got home, the chances are I could have read it wrong or something daft like that but I can't be sure so I'll have to go back and retest.
 
Hi All

So I've just extended two circuits and I've got home to type my results up for the certificate and I'm doubting my results, For the R1+R2 for the cooker circuit I got 0.02 ohms and for the ring I got 0.25 ohms, something seems a little off here.

Now by my calculations a 6mm cable should be giving me approx 0.03 per meter and the run to the board is approx 10m so i'm tinking my tester needs to go to be looked at, what do ya rekon?

Most probable that your MFT is not very accurate at low readings such as this. The R1+R2 of 6mm/2.5mm twin and earth cable should be 10.49mOhms/metre though according to OSG values.
0.25 Ohms for the R1+R2 of a ring final seems a perfectly reasonable result for an average sized house.
 
It's worth making or buying a simple calibration box. All you need is a couple of low value resistors (say 0.5 ohms or less and 1 ohm)and a 10 meg resistor,it's a simple matter then to verify your meters consistency on site.
I made ours for less than a tenner out of the above resistors,some brass M4 bolts and a 4x4 plastic box.
 

Reply to Unusually low R1+R2 readings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

After fixing a few CPC related issues on a ring final I got the following results L-L = 0.47 N-N = 0.47 CPC-CPC = 0.69 R1+R2 Tested at 0.31...
Replies
3
Views
1K
Have only recently gotten in to testing. Doing an R1+R2 on a lighting circuit but instead of producing a result my tester clicks over and over...
Replies
5
Views
917
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
887
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock