Just had a quick run through the document it does seem to be addressing a lot of the issues that have been discussed a number of times on this forum, including mounting systems, loading, wind loading etc - also covers the competent person scheme building regs etc, - seems like the MCS scheme will use this to enforce regulations rather than their own documents - possibly a good thing.

Comments on distance from edge of roofs like:
"For a domestic roof, a suitable minimum clearance zone is around 40-50cm." - it then goes on to explain why


It lists these changed areas:
* Notification to DNO’s referencing changes to Engineering Recommendations G83/2 and G59/2
* Updates to BS7671
* Earthing & Bonding
* Application of RCD’s
* Performance estimates
* Wind uplift calculations



Some inital comments - these are just thoughts and would welcome a debate!

Change: Array Earthing or Bonding:
Flowchart clarified, simplified and comprehensive guidleines given.

Result: Simple to follow guidelines.


Change: AC Isolation:
An accessible means of isolation shall be provided to isolate the a.c. circuit . MCB’s, RCD’s and main switches installed in accordance with
BS7671 and in an accessible location can be used to fulfil the requirements for an accessible means of isolation

Result:
Means that only an MCB needs to be provided at connection to the incoming mains - no seperate isolators.
** MCBs are allowed by BS7671 to be used as a means of isolation (Table 53.4 - was Table 53.2) (for TT or IT it'll need to be adouble pole one)

Incoming=>Meter=>MCB=>Total Generation Meter=>Lockable in off position only isolator Near Inverter=>Inverter

Presumably it could also be TotalGeneration Meter=>MCB

And, is a single pole MCB acceptable? - it appears to be so (see also the updated example configuration diagram)


Change: RCD Protection:
Cleared up, simple flow chart so SMA, Fronius, Power-One etc OK and correct with the advice they have been giving.


Also, see this:
"The final connection into a distribution board that contains one or more circuits protected by an RCD, shall be made in such a way that the outgoing circuit for the PV system is not connected into the outgoing side of an RCD installed for the protection of other circuits (ie in a split board – connected into the part not protected by the RCD) ."

Result:
So generally it would not be RCD protected, if it needs to be then it needs it's own RCD of the correct specification.


Change: Output Calculations:
Upside: SAP Replaced with a more accurate analysis, location, azimuth, inclination, shading.

Downside: Still ignores panel and inverter performance.
 
Incoming=>Meter=>MCB=>Total Generation Meter=>Lockable in off position only isolator Near Inverter=>Inverter

Presumably it could also be TotalGeneration Meter=>MCB

I'd leave it as it is. That makes it easier to isolate the TGM if it ever needed to be changed.
 

Reply to Updated PV Guide out for Consultation in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
414
Hi all, I hope you can help me please. I had solar system installed nearly 2 months ago and my installer turned out to be cowboy despite having...
Replies
14
Views
5K
Hello there, I’m in the process of mapping out a relatively standard S-plan system for my parents central heating and hot water system. Not sure...
Replies
10
Views
2K
Hi Everyone, Hope you’re all well! I’m wondering if anyone is able to shed some light on a situation I’m having with my neighbour. I received a...
Replies
21
Views
5K
Hi, hopefully, you can help me by giving some guidance over the EICR which has failed for my rented property. It was carried out by an electrician...
Replies
16
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock