Search the forum,

Discuss Upgraded db regulations in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
2
We have came across an upgraded db, the installation about 20 years old, and this db change happened this year.

The db as not been bought up to 18th edition regulations and just been swapped like for like.

We are carrying out a EICR on this db, I understand the db should off had a EIC but this was from another company. Would you code 2 all the non compliance with the 18th edition? No rcd on sockets and no rcd on lights within shower area, remembering the installation 20 years old but just had a new db.

Thanks
 
The fact that the new work doesn't comply with the 18th Edition shouldn't affect how you code the observations - this is an assessment of the safety (or otherwise) of the installation. So once you've assessed the severity of the non-compliance then which Edition/Amendment of the Regulations was in force at the time really isn't relevant.
 
In my mind the whole point of the EICR coding is the danger, not if it matches current regulations or not.

I would follow the Best Practice Guide #4 for coding as it is a justifiable stance in all cases (so C2 for lack of RCD only if supplying outside sockets, etc).

EDIT: Just beaten by @Risteard !
 
Does it count as like for like replacement / maintenance?
Might not have needed a certificate at the time.
Who knows what modifications have been carried out on the installation in the previous 20years (compliant or otherwise).
A replacement DB always requires testing and an EIC in my book, and Part P notification.
Certainly not as simple as changing a 'like for like' light fitting!
Not sure I've ever done a 'like for like' db change as there is always (or seems to be) some upgrade!
 

Reply to Upgraded db regulations in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

EICR installation 40 + years old… cabling PVC T&E… no MBPC… As stated fuses, all ELI measurements are ok… RCD separate from DB/CU 30ma, what’s...
Replies
2
Views
1K
Hi all, as in the picture, when connecting a 230V cable to a db like this, is there a legal requirement to install external RCD unit? Also, if the...
Replies
15
Views
2K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
23
Views
994
Morning guys, I would like some advice, currently at my workplace, I am replacing a DB and existing wiring in a warehouse. One of the ways feeds...
Replies
4
Views
1K
Just had an EICR done and C2 (dangerous) applied to 3-way consumer unit which is exclusively for 3 x Storage Heaters. Pic below. Yes its plastic...
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top