Hello guys

On a 24v circuit i use a link between lots of io to test inputs.

Can i use the multimeter to short the terminals like a link (copper wire) if so what setting would be best. I know boltage reading doesnt act like a short. But not sure to try anything else encase i break the thing lol

Never used a multimeter todo this before. Only to read voltage lol
 
If this is a SCADA system or similar you can use some voltage verification units to put a 4k ohm load across the inputs. If it is a common mode input you can tie one end down to the common and run through all the inputs very quickly.
It also safe in case you accidentally catch the probe on a supply terminal.
 

Reply to Use multimeter to short io in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I've installed a Lorex doorbell recently, but it is not turning on. I did some tests using a multimeter and this is what I found...
Replies
5
Views
1K
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K
Hi! Some help would be appreciated! I've just moved into new house, wanting to check insulation resestance etc as getting some nuisance...
Replies
2
Views
338
I was working alongside the plumber yesterday. I had to drill some 32mm holes through joists. I always use my Makita 481 high torque drill will a...
Replies
29
Views
2K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock