Discuss Using armouring as earth and RCD protection in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hi,

If an SY cable is used to supply a consumer unit, and there isn't a guaranteed depth of 50mm for the wall it is in, would using the braiding as the earth negate the meed for RCD protection of that cable?

Thanks
 
The problem, or at least one of the problems, with SY cable is it is not to an BSI standard, so its use for wiring and in particular "fixed wiring" is strongly discouraged.

In the application you are asking about you would need to know that the braid was able to handle the fault current / energy to open the supply fuse/breaker without allowing the penetrating nail, etc, to become isolated and only in contact the the live conductor. I don't think any SY has such a rating.

If you don't want to use SWA due to its stifness and specific gland requirements then an alternative that is rated for some breaker use (to 20A C-curve I think) if Flexishield cable. it is pretty nice to work with as well as being UV resistant and not often nibbled by rodents.
 
No, because the braid on SY is only for reasons of electromagnetic shielding and no way goes near the criteria for mechanical protection. And that’s even before we’ve gone to the ‘SY’ conversation.
 

Reply to Using armouring as earth and RCD protection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
861
Greetings, I am homeowner and looking to confirm if I will need earth boding to water pipes. There is already earth boding near Gas meter and the...
Replies
23
Views
925
Hi everyone, I wondered if anyone could help me with something that has been niggling me please?! When a Solar PV feed in circuit is installed...
Replies
14
Views
2K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock