Discuss Varilight Dimmer max loading in the UK Electrical Forum area at ElectriciansForums.net

Right, the lamps ive chosen have a running current of 65mA, start up is 10 times the running current so thats 650mA or 0.65 A, times this by 24 equals 15.6a inrush. Convert this to watts equals 3588w. So this means I need a dimmer that is rated to at least 3588w (4Kw) to withstand the inrush ! Thats correct isnt it ?
 
What about a current limiting load in series with all the LEDs? Our typical 3kW immmersion heater element will limit the inrush to 13A peak and only drop 10V - 20V when the lamps are all running. My contribution to Halloween and Guy Fawkes Night :D .
 
Last edited:
I notice you rated my comment as optimistic....Do you think one of these will do the job?https://www.downlights.co.uk/media/mconnect_uploadfiles/v/-/v-com-dimmer-instructions.pdf like someone has mentioned above.

I gave you an optimistic because its not your thread - this one, and the previous lack detail and seem to lack considered response.

I would be starting with OEM's that make LED dimmers - and not via wholesalers - by contacting them directly .......... with as many known facts as possible and asking for their input

AND warning the customer that this may not be as easy as end users often think ......

As for the V-Pro - no idea mate ........... best ask them.......... but I don't like them
 
I notice you rated my comment as optimistic....Do you think one of these will do the job?https://www.downlights.co.uk/media/mconnect_uploadfiles/v/-/v-com-dimmer-instructions.pdf like someone has mentioned above.

The link there does state for a 400w dimmer the max number of led's is 40, but it dont state a wattage ! Supposing it means 40 x 10w, thats bang on max loading which I would not like. Also consider the reply from varilight (as someone posted earlier) to use only 75% of the dimmers load, and also consider the good practice rule of thumb of using only 10% of the dimmers capacity (as shown in my earlier post); it does make you wonder if anyone really knows (including Varilight) what they're talking about,.
 
I gave you an optimistic because its not your thread - this one, and the previous lack detail and seem to lack considered response.

I would be starting with OEM's that make LED dimmers - and not via wholesalers - by contacting them directly .......... with as many known facts as possible and asking for their input

Dont know how you come to a conclusion that my
AND warning the customer that this may not be as easy as end users often think ......

As for the V-Pro - no idea mate ........... best ask them.......... but I don't like them

Not sure how you assume my two posts lack considered response and lack detail. The OP questions are what they are, the threads end up going round the houses cause people chime in with response that veers off the path, !
 
Last edited:

Reply to Varilight Dimmer max loading in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I currently have 4 JCC LED down lights in my bathroom with a 2 gang dimmer on the outside. The first dimmer switch controls the LEDs and...
Replies
6
Views
2K
I am looking at installation of an architectural dimmer, that is will supply 6 channels, with 20A circuits each (2400W ea). Our hall has can light...
Replies
2
Views
690
This week I nearly learned a hard lesson re this!! (using a Lutron RA2 inline dimmer to control 6x 700ma 13w LED fittings)...
Replies
4
Views
1K
Hello everyone. Thank you in advance for any help you can provide. I tried installing a dimmer to a 3-way circuit. The dimmer has a hard...
Replies
3
Views
1K
Having a bit of a nightmare with what should have been a simple job. Back in January I replaced some old Varilight dimmers which had failed after...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock