Hi, hope someone can advise. Ive just called Varilight helpline in regards to max loadings on their 300w trailing edge LED single gang dimmer. They tell me that I can have a maximum of x30 10w leds on the dimmer.

Most info out there regarding dimming LED suggests to divide the dimmers wattage by 10 to determine max number of led lamps; I put this to the guy at customer services and he says varilight dimmers are designed differently and can handle the x30 10w lamps. Can anyone confirm or reject this statement.

I never think its a good idea to load dimmers to max like this; the guy at helpline says the inrush of x 30 10w led's wont effect a 300w dimmer, im not so sure.
 
I think they have given you incorrect information. Your calculation of dividing by 10 is a common method, as you say divide the 300w by 10 to give a maximum led loading of 30w.
 
I think they have given you incorrect information. Your calculation of dividing by 10 is a common method, as you say divide the 300w by 10 to give a maximum led loading of 30w.

That was my thoughts also Westy, just that the guy at technical services seems adamant I could load it with 30 leds. Just wondered if anyone had done this and what the results were. Technology moving so fast now its a pain to keep up
 
If it's a vPro series, the datasheet for the JQP401W suggests a maximum of 10 LED lamps upto 120w.

I wouldn't worry too much about in-rush current as many of the Varilight dimmers use a soft start when the power is applied.
 
I had no end of problems on one job where we’d fitted total of 50 10w led split across multiple banks.
The led suppliers then put list of faulty fittings out.
I tried every single dinner mod and spoke with every single manufacturer.
Varilight told me not to put more than 75% led loaf in their mods. Which beggars belief that they sell them under the guise that they’re capable of more than is stated on the packaging.
 
How many LED's are you planning on adding in total on the circuit?

JCC have advice on the maximum numbers per circuit on their installation instructions
 
Thats 'cos they can't handle the latent warranty issues in a few years months time. :)

Hit, Nail and Head spring to mind ..............

JCC have lost me as an installer and I didn't see them at Elex today either - I wanted to have a word with them about their inability to provide warranty replacements a few months after discontinuing a product so whats going to happen in a couple of years????????
 
Hahah we tried zano. £50 dimmer and suppose to be the dogs do do. Didn’t work

Most of the sealed unit manufacturers have a compatibility list of dimmers with their products. I'd follow that routes when picking and choosing.

I've gone off sealed units nowadays, not that I'm installing anything now.
 
Hit, Nail and Head spring to mind ..............

JCC have lost me as an installer and I didn't see them at Elex today either - I wanted to have a word with them about their inability to provide warranty replacements a few months after discontinuing a product so whats going to happen in a couple of years????????

I installed some 7's for my brother about 5 years ago. He's replaced one himself, then another went last month. I emailed their tech support, 'cos the 7 is no longer made. He never registered them. Fair play after a few email exchanges, they sent him a FGLED6 FOC. Luckily he had non dimmable ones. Dunno if they would have been so obliging otherwise.
 
And another customer of mine, I replaced 13 of his old 12v downlights, as he was fed up replacing the transformers every few months.

Fit these new fangled FGLED6's, fit & forget I said. That was about 4 years ago.

I've replaced 12 of them, so far! Luckily he registered them. When one goes now, he just rings them up, and they send one in the post.
 
I installed some 7's for my brother about 5 years ago. He's replaced one himself, then another went last month. I emailed their tech support, 'cos the 7 is no longer made. He never registered them. Fair play after a few email exchanges, they sent him a FGLED6 FOC. Luckily he had non dimmable ones. Dunno if they would have been so obliging otherwise.

I always did the registration on behalf of my clients, in their name .....
 
Murdoch, its going a bit off track here. Currently the existing circuit is on one switch operating x24 100w filament lamps; they want them changed to led's and also to be able to dim them, hence my OP :)

That’s fine but you did say switches and this thread is almost identical to a recent one of yours .......

As I have previously stated, if you plan to replace the existing 24 x 100w filament bulbs with LEDs you need to be wary of inrush currents .......

What is the MCB?
 
Murdoch, its going a bit off track here. Currently the existing circuit is on one switch operating x24 100w filament lamps; they want them changed to led's and also to be able to dim them, hence my OP :)

Murdoch does have a point. The current set up works and they can dim them.

Installing 24 LED's on one circuit, with one dimmer needs some consideration. Otherwise you might rule the day you changed things.
 
That’s fine but you did say switches and this thread is almost identical to a recent one of yours .......

As I have previously stated, if you plan to replace the existing 24 x 100w filament bulbs with LEDs you need to be wary of inrush currents .......

What is the MCB?

The MCB is a 16 A type C, im fairly sure this would handle the inrush.
 
Murdoch does have a point. The current set up works and they can dim them.

Installing 24 LED's on one circuit, with one dimmer needs some consideration. Otherwise you might rule the day you changed things.

OP - PLEASE take note of this reply ...............
 
In a nutshell the existing circuit has 24 lamps on one switch, three times (theres 3 separate circuits each with a 16a CB). So im looking for a dimmer that can handle x24 (9-10w) leds !, if i cannot find one then I will get a mode lighting power pack but they are a bit pricey
 
In a nutshell the existing circuit has 24 lamps on one switch, three times (theres 3 separate circuits each with a 16a CB). So im looking for a dimmer that can handle x24 (9-10w) leds !, if i cannot find one then I will get a mode lighting power pack but they are a bit pricey

I read this as 72 lights on 3 separate circuits - 24 per 16A type C breaker

Yes? No?

What is this facility - a community hall or similar?
 
Right, the lamps ive chosen have a running current of 65mA, start up is 10 times the running current so thats 650mA or 0.65 A, times this by 24 equals 15.6a inrush. Convert this to watts equals 3588w. So this means I need a dimmer that is rated to at least 3588w (4Kw) to withstand the inrush ! Thats correct isnt it ?
 
What about a current limiting load in series with all the LEDs? Our typical 3kW immmersion heater element will limit the inrush to 13A peak and only drop 10V - 20V when the lamps are all running. My contribution to Halloween and Guy Fawkes Night :D .
 
Last edited:
I notice you rated my comment as optimistic....Do you think one of these will do the job?https://www.downlights.co.uk/media/mconnect_uploadfiles/v/-/v-com-dimmer-instructions.pdf like someone has mentioned above.

I gave you an optimistic because its not your thread - this one, and the previous lack detail and seem to lack considered response.

I would be starting with OEM's that make LED dimmers - and not via wholesalers - by contacting them directly .......... with as many known facts as possible and asking for their input

AND warning the customer that this may not be as easy as end users often think ......

As for the V-Pro - no idea mate ........... best ask them.......... but I don't like them
 

Reply to Varilight Dimmer max loading in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I currently have 4 JCC LED down lights in my bathroom with a 2 gang dimmer on the outside. The first dimmer switch controls the LEDs and...
Replies
6
Views
2K
I am looking at installation of an architectural dimmer, that is will supply 6 channels, with 20A circuits each (2400W ea). Our hall has can light...
Replies
2
Views
715
This week I nearly learned a hard lesson re this!! (using a Lutron RA2 inline dimmer to control 6x 700ma 13w LED fittings)...
Replies
4
Views
1K
Hello everyone. Thank you in advance for any help you can provide. I tried installing a dimmer to a 3-way circuit. The dimmer has a hard...
Replies
3
Views
1K
Having a bit of a nightmare with what should have been a simple job. Back in January I replaced some old Varilight dimmers which had failed after...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock