Hi all - when testing ring final continuity in a small shop the other day my Megger 1720 wouldn't carry out the test and displayed "VOL O-L" on the L and N legs (CPC was OK). I believe this message is due voltage present on the cables....MCB was off. When switching the board off at the main switch the circuit was reading open on both legs.

Obviously I have a discontinuous ring that would need investigating...but usually the meter will just read >999 and not VOL O-L.....so my question is, is the VOL O-L error due to induced current from adjacent circuits or is there likely to be something else going on here?

Many thanks - Bill
 
Hi all - when testing ring final continuity in a small shop the other day my Megger 1720 wouldn't carry out the test and displayed "VOL O-L" on the L and N legs (CPC was OK). I believe this message is due voltage present on the cables....MCB was off. When switching the board off at the main switch the circuit was reading open on both legs.

Obviously I have a discontinuous ring that would need investigating...but usually the meter will just read >999 and not VOL O-L.....so my question is, is the VOL O-L error due to induced current from adjacent circuits or is there likely to be something else going on here?

Many thanks - Bill


Just checked the manual on google VOL-O-L is voltage overload
 
It is a safety element on your Megger which stops you testing further you will have to find out why and how much voltage is present and eliminate it before yo can continue,

You will get the same when IR testing im affraid



1

5
 
Hi Bill, I've had this a few times on my 1730. I think you'll find it may be phantom/induced voltages, being sensed by your MFT, IMO. The MFT reacts to these voltages with different error messages, depending on the test being carried out, in my experience. As you've said, when you've isolated the whole installation, the MFT carries out the test.
The only way to be sure, is testing the circuit for voltage with an analogue tester, or meter not affected by phantom voltages.
Iā€™ve found Megger technical quite helpful, to explain the error codes the MFT displays, as the manual is a bit unclear. I have the name of a particularly helpful guy, on another PC. Iā€™ll PM youā€™re his details in acouple of days.
 
Last edited:

Reply to VOL O-L on Megger 1720 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
713
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
834
what the showed on the megger tester vol o-l, doing a EICR on a flat and doing continuity testing every thing isolated and then head in a spin...
Replies
2
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock