Discuss volt drop rule of thumb in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

ive just found my 16th edition OSG, so used the resitance values there. my above calc works oncables rated at 70degrees c. does anybody have the derating factors for other temps? thanks,


john
 
i am a bit stuck on volt drop myself, could someone break it down a bit for me please

i is the design current ie 300w

r is the resistance say 10m x 2.5 7.41 x2 x100 x1.2x10/1000 = 0.178

v = ixr 300w x 0.178 = 53.4 volts?
 
Last edited by a moderator:
i am a bit stuck on volt drop myself, could someone break it down a bit for me please

i is the design current ie 300w

r is the resistance say 10m x 2.5 7.41 x2 x100 x1.2x10/1000 = 0.178

v = ixr 300w x 0.178 = 53.4 volts?


Design current (Ib) isn't measured in watts, it's measured in amps i.e 300W ÷ 230V = 1.3A (I = P ÷ V)

Volt drop = (mV/A/m) x Ib x L so for 10m of 2.5mm² carrying 1.3A it would be (18 ÷ 1000) x 1.3 x 10 = 0.23V
 
Last edited by a moderator:
Design current (Ib) isn't measured in watts, it's measured in amps i.e 300W ÷ 230V = 1.3A (I = P ÷ V)

Volt drop = (mV/A/m) x Ib x L so for 10m of 2.5mm² carrying 1.3A it would be (18 ÷ 1000) x 1.3 x 10 = 0.23V

how do you get the 18 figure?
 
From the Volt Drop table in BS 7671 for 2.5mm²

ok just got that so 20m x 2.5 and 300w load

300/230 = 1.3a

v = ixr

18/1000 x 1.3 x 20 = 0.46v

so in the exam they are going to provide you with the volt drop table figure i assume?
 
Last edited by a moderator:
ive just found my 16th edition OSG, so used the resitance values there. my above calc works oncables rated at 70degrees c. does anybody have the derating factors for other temps? thanks,


john

Here's a tip. Remember this...


The rating factors for cable and ambient temperatures are worked out like this:

For a rise or fall in temperature you multiply or divide by 1 + (0.004 x temperature difference).

That's where the 1.2 comes from.

You start with a resistance at 20°C and then multiply it by (1 + (0.004 x 50)) to get to 70°C (0.004 x 50 = 0.2). 50 is the temperature difference between 20°C and 70°C.

And the other way, if you start with a resistance at 70°C, this time you divide by (1 + (0.004 x 50)) to get to 20°C.
 
im remebering the theory now, from AC theory in college. Ro=1x fish shaped symbolxt.

cheers mate.

great help.

its one thing learning the formulae, but another about knowing when to put it in practice.
 

Reply to volt drop rule of thumb in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, I'm looking for a bit of advice on a volt drop query we have in our office. I'll explain the scenario and I would really appreciate any...
Replies
3
Views
634
Hi, go easy on me please, I've just returned to the trade, well I am about to, I received my Gold Card last Thursday. I've been gen'ing up for a...
Replies
4
Views
886
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
Hi everyone :) my first post here. Quick background I'm a newly qualified installer of somewhat advanced years whose just starting out in the...
Replies
12
Views
1K
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
411

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock