soulman

-
Arms
Reaction score
94
Hi,

I was calculating volt drop today using xlpe armoured cable, 3 core, single phase. Table 4E4A pg 373. I am using 3 core cable but on single phase, so i would assume column 3 for single phase. I was told by the tech helpline although the cable is being used for single phase that column 4 should still be used as it is the number of cores that is the factor. Can anyone tell me why?

Cheers
 
Theoretical the third core can affect the current carrying capacity of the other two cores as it restricts heat dissipation which would increase the conductor resistance but I would say it is negligible. There is a case that for Table 4E4A for the current carrying capacity you should use the columns for a three phase supply if you are using a three core cable on single phase, again I would think this is negligible, I suspect this is the reason.
 
Theoretical the third core can affect the current carrying capacity of the other two cores as it restricts heat dissipation which would increase the conductor resistance but I would say it is negligible. There is a case that for Table 4E4A for the current carrying capacity you should use the columns for a three phase supply if you are using a three core cable on single phase, again I would think this is negligible, I suspect this is the reason.
What he said
 
but he's referring to VD, not CCC.
Yeah I know but the voltage drop would be affected by the third core restricting heat dissipation. I added the ccc bit because it has the same affect.
Looks like I worded it poorly.
 
Last edited:
Hi, Thank you for replies. After looking into this further, I have decided that the tech line was incorrect. The column that should be used, is column 3 for single phase. The third conductor will only carry current under fault conditions, therefore having no bearing on volt drop.

Cheers
 
Hi, Thank you for replies. After looking into this further, I have decided that the tech line was incorrect. The column that should be used, is column 3 for single phase. The third conductor will only carry current under fault conditions, therefore having no bearing on volt drop.

Cheers
I agree with them though the effect of the third core would be debatable.
 
Hi Westward, i spoke to an electrical designer. He told me, if I look in the regs, i'll see that there is no difference in volt drop between between 3 or 4 core cable as it is presumed that 4 core will be supplying 3P & N. The load should be balanced therefore no current flowing in the neutral, 4th core.

Cheers
 
Originally you were using three core for single phase with the third core as a cpc and as such columns for three phase should be used due to the negligible effect of the third core.
As for a three phase circuit being balanced and the neutral carrying no load may work in Utopia but in practice this is highly unlikely. Whether it carrys load or not its presence will affect the other conductors.
 

Reply to Volt Drop table help in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, Just looking for some advice: I'm in the process of updating an old cable calc spreadsheet that helps to spit out Zs and Voltage Drop...
Replies
8
Views
885
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
Hi All, From what I understand, working out the design current - Ib for single phase is quite easy (max appliance power/voltage). For three...
Replies
7
Views
1K
Hi, go easy on me please, I've just returned to the trade, well I am about to, I received my Gold Card last Thursday. I've been gen'ing up for a...
Replies
4
Views
864
Hello, New trainee electrician so sorry if this is a dumb question I feel confident with calculating the volt drop for a ring and radial circuit...
Replies
2
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock