Discuss Voltage Drop Equation in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

N

Noob2013

Hi,

I've been doing some revison and came across 2 different equations for voltage drop.

The first one is;

Vd = mV/A x Ib x L divided by 1000

The second one is;

Vd = (R1 + R2) x Ib x Multiplier

The multiplier is to compensate the difference in conductor temperature at the time of the test and the normal operating temperature of conductors when maximum resistance. 1.2 multiplier for 20 Degrees Celsius.

Are these both correct?

Thanks
 
mV/A/m in the first example. this is taken from bgb or osg tables.

second example is basic ohms law V=IR. ( with the multiplying factor for temp. taken into consideration.
 
Hi,

I've been doing some revison and came across 2 different equations for voltage drop.

The first one is;

Vd = mV/A x Ib x L divided by 1000

The second one is;

Vd = (R1 + R2) x Ib x Multiplier

The multiplier is to compensate the difference in conductor temperature at the time of the test and the normal operating temperature of conductors when maximum resistance. 1.2 multiplier for 20 Degrees Celsius.

Are these both correct?

Thanks

Tel has explained it well, so i wont expand. But i will give you a couple of whys and what fors.

The (mV/A/M) x Ib x L /1000 would be the calculation used by the designer at the design stage of a new installation.

Method 2, (R1+R2) x Ib X 1.2, this would be used on a periodic inspection and test, when the tester would need to do the calculation and the circuit length is not known.

The 1.2 is to account for the temp difference between the live conductors.

Cheers............Howard
 
Tel has explained it well, so i wont expand. But i will give you a couple of whys and what fors.

The (mV/A/M) x Ib x L /1000 would be the calculation used by the designer at the design stage of a new installation.

Method 2, (R1+R2) x Ib X 1.2, this would be used on a periodic inspection and test, when the tester would need to do the calculation and the circuit length is not known.

The 1.2 is to account for the temp difference between the live conductors.

Cheers............Howard


That needs expansion! :)
 
they will expand as they warm up.i'll get my coat. :waving:
 
Hi all in the forum
I was browsing his thread, andas the OP appears to be a student I thought I would correct the errors beingmade in the answers regarding the second formula. The first is perfectlyok for calculating volts drop but the second is not. R1 is the resistance ofthe line cable ad R2 is the resistance o the cpc., therefore R2 is not part ofthe volts drop calculation. It should be replaced with Rn (the resistance ofthe neutral cable). The 1.2 multiplier is used in a 70 degree thermoplasticcable to take into account that the cable could be loaded to itsmaximum current carrying capacity. I believe that R1+R2 equations canbe used when evaluating Zs
 
Hi all in the forum
I was browsing his thread, andas the OP appears to be a student I thought I would correct the errors beingmade in the answers regarding the second formula. The first is perfectlyok for calculating volts drop but the second is not. R1 is the resistance ofthe line cable ad R2 is the resistance o the cpc., therefore R2 is not part ofthe volts drop calculation. It should be replaced with Rn (the resistance ofthe neutral cable). The 1.2 multiplier is used in a 70 degree thermoplasticcable to take into account that the cable could be loaded to itsmaximum current carrying capacity. I believe that R1+R2 equations canbe used when evaluating Zs

well spotted there. should be Rn. however the tabulated value of R1+R2 can be used where the cpc is the same size as the line conductor, e.g. with SWA or singles.
 

Reply to Voltage Drop Equation in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm...
Replies
2
Views
729
Hi! Once you've calculated the voltage drop in Volts - you divide by 400V for three phase right? For example: three phase 30kW appliance, 10mm...
Replies
5
Views
2K
Hi All, Just looking for some advice: I'm in the process of updating an old cable calc spreadsheet that helps to spit out Zs and Voltage Drop...
Replies
8
Views
887
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
Hi there, I'm Currently doing my design calcs for my college project and doing the actual Zs calculation. Formula is Zs= Ze (or Zdb) + (R1+R2)...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock