Hi everybody.

I have a question (still learning, passed 17th edition and part P, but I'm not yet registered).
If you use formula from On-Site Guide p.140 what the design current you put in the formula, to calculate max length of cable for 11.5V.
If 32amp then the maximum length of ring final would be around 20metres (both legs parallel) or 16 amps and then around 40 metres in total length of 2.5mm cable.

If this is right how would you wire second floor socket circuit if CU is in the basement (40 metres not quite enough for 3 rooms on 2nd floor).

Hope someone can explain.

Thanks
 
For volt drop on a ring final the formula is

mV/A/M x ib x L / 1000 / 4

And for maximum length it is

L = 4 x max vd x 1000 / ib x mV/A/M

Try a value of 20A for your design current and work it out.
 
Ok. Just can't figure out where the "4" comes from.
I found table 7.1 in On-Site Guide which is probably what I was looking for.
It says this table has been designed to enable a radial or ring final circuit to be installed without calculations.
 
the divide by 4 comes from the same place as with R1+R2 measurements for a RFC. because its a ring, you divide by 2 because the you need the value at the mid point, and then again as you have 2 cables in parallel, sharing the load.
 
It can be but think says 90m for rfc in osg where if you work it out you can make it longer..

The 4 comes from double the CSA (2legs) and have the distance to teturn
 
Easy way of thinking about it is a follows: VD = mv/a/m x ib x length / 1000 so if its a ring just divide the ib in half and the length in half or (divide all of it by 4), try it, it works :)
 
Volt Drop = 18mv/a/m x 32amps ib x 50 mts length /1000 / 4 = 7.2 volts or Volt Drop = 18mv/a/m x 16amps ib x 25 mts length /1000 = 7.2 volts, take your pick.
 
Sort of. As I can't get values for 5mm cable but work out estimated it's about right. Take voltage drop as 8.5 and Ib 30amps it is roughly 90m.
 
Yarcyk, I am trying to explain to you how the (4) number is derived, the worked example I gave you is a worked example to help you understand!
 
Sort of. As I can't get values for 5mm cable but work out estimated it's about right. Take voltage drop as 8.5 and Ib 30amps it is roughly 90m.

Why mess about trying to make up formulae when you have been given the correct ones in post #2
 
did read it. switch goes after the CU and before the light. if it's a ring circuit, however, you need to fit 2 switches. 1 in each leg. :stupid:
 

Reply to Voltage drop question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi Guys, I'm doing my Level 3 C&G design project and just have a few design related queries which i am so far struggling to find clarity on...
Replies
0
Views
3K
Hi all. Constant current LED lighting is a new concept to me. Not that difficult to get the head around, but I cannot find an answer to the...
Replies
9
Views
5K
I thought that I posted this in the DIY part of the forum but I believe I did not. I am sorry about that. I put in a 10' x 20' metal shed about...
Replies
2
Views
1K
Hi Folks I've been trying to work out whether a doorbell will work with approximately 16m run of bell wire. I've tried to find out volt drop...
Replies
6
Views
7K
This is my first post so please be gentle! I've been asked to extend an RFC into an extension at the back of an 8 year old property. It is a...
Replies
24
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock