Discuss Voltage dropping in a domestic house as you use more appliances ? in the UK Electrical Forum area at ElectriciansForums.net

B

Bern1e

Hi folks!
Any answers on this problem?
I attended site and was told various items of equipment caused the rcd to trip randomly,after checking the Ze and voltage I tested the rcd which wouldn't trip x1 or x5.
I then deemed this faulty and replaced the rcd only to find this also did not trip.
I then decided my tester might not be working so i used another and the same problem occurred,by this point I am pulling my hair out.
After testing the supply voltage I noticed that when more appliances were plugged in the voltage decreased.
It was also noted the rcd would test on the incoming supply cables end but not the busbar side.
I m now deciding t become a brick layer !!!!!!!!
Help please me thinks uk power networks problem and loose neutral there endis the issue.
 
What voltage did you initially get when you tested without load? How low did the voltage drop when load was applied? Did the voltage drop below the acceptable minimum?
 
Ensure when you are running your bricks you have set a guide line up to keep your run level, use a good cement mixture and don't rush it until you have gained the expertise of a well seasoned brickie... hope that helps ;)
 
Was this site in a rural location possibly at or near the end of an overhead supply , I have seen a very similar situation where I live especially when off peak supplies are switched in. if this is what your finding then yes its UK power networks issue , what is the lowest reading your getting ...
 
If you got 190V and there is no sign of buring anywhere call the power company. Before you do call them measure across the incoming terminals of the CU, and check it is all ok.
 
Maybe also measure a neutral-earth voltage when it's under load and the voltage drops and take your measurements at the first available point in the premises. This might help indicate a supplier neutral issue.
 

Reply to Voltage dropping in a domestic house as you use more appliances ? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
I am not an electrician but am looking for some advice as to how to fix my sporadic light flickering problem that has come and gone for the year...
Replies
24
Views
2K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
725
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
735

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock