Discuss Walk In Freezer in the Electrical Appliances Forum area at ElectriciansForums.net

Dependent on the freezer temp, you may have to source gear rated beyond the normal temp' tolerances of standard cables and plastics.

PVC for instance shouldn't be worked/installed with temp's less than 5c it can tolerate usually to -20 but won't be resistant cracking if moved or knocked etc...

Last walk in fridges I did was done in TPE insulated cable good and flexible to -40c and it was -22c in the fridges, can be sourced from specialist cable brands like LAPP or IGUS.
 
Last edited:
Can't you install the FCU outside the freezer? Preferably install the PSU external as well and just run the ELV supply into the freezer. It would save a lot of hassles if you can. As already mentioned pressure washing, low temperatures and condensation due to very high relative humidity are all considerations.
 
What's this PSU for? If it's for a CCTV camera or trapped person alarm you'd be better off having as much of it outside the freezer as you can.
 

Reply to Walk In Freezer in the Electrical Appliances Forum area at ElectriciansForums.net

Similar Threads

Hello everyone, We had an electrician over, who fitted a 40a MCB in the house consumer unit to supply a new build garage. It's underground SWA...
Replies
14
Views
1K
Hi, I have a client with a small caravan site, approx 5 hookups. His old toilet block was nothing much more than an old shed. He's now 'upgraded'...
Replies
2
Views
558
I have Liebherr fridge freezer and need to extend the cable from the appliance to the wall plug. The directions do not allow an extension lead to...
Replies
2
Views
829
I decided to get solar panels, the inverter instructions say one can use type AC, so the existing 14 x RCBO CU seems OK, may be a good idea to fit...
Replies
4
Views
1K
I have a 7 year old integrated Neff K42 fridge freezer and I need to replace a couple of the attached kitchen cabinet doors hinges. In order to...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock