I understand the long lead test of water and gas. Dis connect end from cu and test between that and connection to extraneous pipe work. Reading has to be below 0.05 Ohms.

Does the pipe work still need bonding if its a plastic incomer?

What about if the house has a mixture of copper and plastic pipework. Do i just long lead test each accessable piece and ensure its below 0.05ohms?
 
If the incoming pipe is plastic I believe that the metal part of the pipe work would not be classed as an extraneous part.

I would bond it as soon as the pipe changes to copper from plastic.
 
I understand the long lead test of water and gas. Dis connect end from cu and test between that and connection to extraneous pipe work. Reading has to be below 0.05 Ohms.

Does the pipe work still need bonding if its a plastic incomer?

What about if the house has a mixture of copper and plastic pipework. Do i just long lead test each accessable piece and ensure its below 0.05ohms?

In the case of domestic house etc, it would be doubtful if you would need to bond the copper sections when the incoming pipe is plastic. On some types of blocks of flats/apartments you may well find that the copper sections after the plastic incoming service pipe would need bonding. So in all circumstances the best approach would be to test the exposed copper pipework. Under 23k ohms and it needs to be bonded back to the MET/EMT!!
 

Reply to Wander lead test. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi guys and gals, I have a question about the leads to computers (commonly known as kettle leads). I am new to PAT testing so please bear with...
Replies
0
Views
957
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
465
Hello, Carrying out remedial work on a commercial site and I've come across a metal out building that has a water supply to it. The water pipe...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock