Discuss Washing machine intermittently trips RCD. Manufacturer declares machine fault-free and suggests faulty home electrics. What should I do? in the UK Electrical Forum area at ElectriciansForums.net

They said I should contact an electrician and ensure that an RCD is fitted with a unit that has a symbol that I can best describe as two curly lines (my RCD doesn’t have this symbol).
On just this small point of your post, this is probably a red herring.

There are several types of RCD - these are the most common you see in domestic, with AC being the most common until recently:

RCDs.png
(Edit: fixed pic)

Some modern washing machines using inverter drives etc, can cause the AC type to not trip as quickly as they they should, because of the DC on the circuit. However, this is the opposite of what you are experiencing. Type A are generally recommended now because they can cope with this.

I'm not aware of washing machines being more likely to trip AC RCDs, though others more knowledgeable may know otherwise.
[automerge]1598899723[/automerge]
Hi thanks
This morning I decided to find out which circuits my devices and appliances are on. My RCD is only labelled with A,B,C,D and numbers. So it was difficult to figure which circuit breaker is responsible for what.
The big thing I've learned today is that all the appliances in the kitchen (microwave, boiler, kettle, washing machine, and fridge, and a small lamp) are all on one circuit breaker. BUT this is not the circuit breaker that trips. All this time I presumed the circuit breaker that trips was responsible for the machine and all the appliances in the kitchen, but it's not the one that trips.

The circuit breaker that trips covers the following:
Wireless router, 19" flat panel TV, small speakers and subwoofer (all three are connected via a four plug extension and are always on/standby)
BT cordless phone main base unit (plugged directly into a mains socket and always on)
Smartphone charger (always plugged in, but turned off at the mains)
Small decorative lamp with five lights, but only one bulb installed (always plugged and switched on at the mains, but never in operation while the machine is running)
Small DAB radio (always plugged in, but turned off at the mains socket)
A small low power single bulb lamp and BT cordless phone charge station (connected via a four plug extension. Always on at the mains. Phone charge station is always on, lamp rarely used never in operation when the washing machine is on)

That's everything that's plugged into the circuit that trips.
A picture of the board would really help. But does the washing machine not turn off when things 'trip'? If it does, then it must be covered by the RCD.

An RCD can cover several 'breakers' and circuits though.

If the washing machine stays on when the RCD/circuit breaker trips, then there is definitely something wrong with the house wiring (or vibration of a nearby cable by the washing machine, so indirect cause as has been mentioned)
 
Last edited:
There is an important contradiction in your info that makes it impossible to advise further without clarification.

In post #1 you said:
I run the machine and it trips the mains just as it was about start up its final spin. I reset the RCD and it completed the cycle from where it was interrupted.
Indicating that the RCD that trips feeds the circuit that the machine is on.

In post #24 you said:
I've just discovered today that the actual circuit breaker that trips isn't the one covering the circuit that the washing machine or any of the kitchen appliances are on.

Either the cycle was interrupted by the breaker tripping or it wasn't. The diagnoses are completely different.

It is possible for an appliance to trip an RCD that does not feed it. The implications are:
1. The likely cause is a neutral-earth fault on a circuit protected by the RCD that trips. It could be in the wiring or an appliance plugged in, which need not be switched on.
2. There is no indication of a problem with the appliance that triggers the trip event, nor the circuit that it is plugged into. It is simply the peak load current (not earth leakage) of the appliance causing the remote, faulty circuit to leak to earth.
3. An electrical test of the affected circuits will almost certainly locate it at once.

I know what my next move would be...
 
On just this small point of your post, this is probably a red herring.

There are several types of RCD - these are the most common you see in domestic, with AC being the most common until recently:

View attachment 60516 (Edit: fixed pic)

Some modern washing machines using inverter drives etc, can cause the AC type to not trip as quickly as they they should, because of the DC on the circuit. However, this is the opposite of what you are experiencing. Type A are generally recommended now because they can cope with this.

I'm not aware of washing machines being more likely to trip AC RCDs, though others more knowledgeable may know otherwise.
[automerge]1598899723[/automerge]

A picture of the board would really help. But does the washing machine not turn off when things 'trip'? If it does, then it must be covered by the RCD.

An RCD can cover several 'breakers' and circuits though.

If the washing machine stays on when the RCD/circuit breaker trips, then there is definitely something wrong with the house wiring (or vibration of a nearby cable by the washing machine, so indirect cause as has been mentioned)
Hi, apologies for the delayed reply.
I was advised by Bosch's technical department to have an RCD with the symbol under the A in your picture. My RCD doesn't have this symbol. I will attempt to get a picture of it.
I can confirm that the washing machine turns off when it trips. What I discovered yesterday was that the washing machine, microwave, kettle, fridge are all on one circuit. But the circuit breaker for this circuit isn't the one that is tripping. My board isn't labelled with "kitchen", "bathroom", "living room", etc. so I had to manually work out what was on each circuit (I didn't do this in all the years I lived here).

What I found was that the circuit breaker that trips when machine is in operation is not the circuit breaker that covers the circuit that the machine is on.

Those electrical devices I listed in my previous post are on the circuit with the breaker that trips. So that's why I am confused because up until yesterday, I thought the breaker that trips is the one responsible for protecting the circuit that the machine is on, but that isn't the case.

Yesterday afternoon, Apart from my TV, wireless router, and speakers, I unplugged all the devices on the circuit with the breaker that trips and ran the machine on a full load two hour 60C wash cycle, followed by an 800rpm spin. It completed both programs without tripping.

What I am confused about is that I only get trips when the machine is in operation. When the machine is not in use everything is fine - no nuisance trips, nothing. Logically when the machine trips the circuit breaker responsible for the circuit that the machine is on should also trip and cut the power. But the circuit breaker that trips and cuts the power is the one responsible for the circuit for those devices I listed in my previous post.

What I wanted to know is can the machine cause the circuit breaker on another circuit to trip? If there is a fault with the machine itself or the circuit that the machine is on, then surely the breaker for machine's circuit should trip. Instead the breaker with all those lower power devices I listed trips and cuts the power.


There is an important contradiction in your info that makes it impossible to advise further without clarification.

In post #1 you said:

Indicating that the RCD that trips feeds the circuit that the machine is on.

In post #24 you said:


Either the cycle was interrupted by the breaker tripping or it wasn't. The diagnoses are completely different.

It is possible for an appliance to trip an RCD that does not feed it. The implications are:
1. The likely cause is a neutral-earth fault on a circuit protected by the RCD that trips. It could be in the wiring or an appliance plugged in, which need not be switched on.
2. There is no indication of a problem with the appliance that triggers the trip event, nor the circuit that it is plugged into. It is simply the peak load current (not earth leakage) of the appliance causing the remote, faulty circuit to leak to earth.
3. An electrical test of the affected circuits will almost certainly locate it at once.

I know what my next move would be...

Hi, sorry for the delayed reply.

Up until yesterday I presumed that the circuit breaker that was tripping every time was responsible for the circuit that the washing machine is on. The breakers aren't labelled and in all the years I've lived here I never bothered to work out which breaker is responsible for which set of sockets and lights, etc. in my home.

I decided to do this yesterday morning and I discovered that the microwave, washing machine, kettle and fridge all sit on one circuit, but the actual breaker that trips when the machine is in operation isn't the one responsible for the circuit that the machine is on.
Instead the breaker that actually trips and cuts the power is the one responsible for the circuit that all those devices I listed in my previous post are on.

I only have this intermittent tripping problem whenever the machine is in operation and when it is in the last 30 minutes of the two hour wash cycle. It can't just be a coincidence that I only get a trip when the machine is in use.

From what I've worked out yesterday, I found that the breaker that trips definitely isn't the one responsible for covering the machine.

The machine still loses power and goes off, but the breaker that actually trips covers a different circuit (the one with all those low power devices I listed).
Logically shouldn't the breaker for the machine's circuit trip if there is an issue with the washing machine?

I don't what to make of it. Could it be that there is a lot earth leakage from one or more of those low power devices and the machine's "natural leakage" causes the breaker on the other circuit to trip?

I didn't think this was possible, but from reading your post it sounds like it is possible for the machine to trip the breaker on another circuit.

I guess the next step isn't going back to Bosch, but calling electrician to find out what's going on.

Many thanks
 
From what I've worked out yesterday, I found that the breaker that trips definitely isn't the one responsible for covering the machine.

The machine still loses power and goes off, but the breaker that actually trips covers a different circuit (the one with all those low power devices I listed).
Logically shouldn't the breaker for the machine's circuit trip if there is an issue with the washing machine?
In many CU (consumer unit = fuse box) there are two types of breaker:
  • One or two RCD (residual current device) to trip on earth leakage, generally electric shock risk
  • 4-12 or so MCB (miniature circuit breaker) to trip on overload, typically a hard fault fire risk
So you will often find one RCD feeds several MCB, and you can turn of each circuit separately via the MCB, but if you do that to the RCD (e.g. the test button) then several circuits go off at once.

I don't what to make of it. Could it be that there is a lot earth leakage from one or more of those low power devices and the machine's "natural leakage" causes the breaker on the other circuit to trip?

I didn't think this was possible, but from reading your post it sounds like it is possible for the machine to trip the breaker on another circuit.

I guess the next step isn't going back to Bosch, but calling electrician to find out what's going on.
The unfortunate thing above the above arrangement is the RCD will trip if it sees somewhere between 15-30mA (1mA = 0.001A) going astray, and that can be due to various reasons that are a fault (bad cable insulation, water getting in to a junction box or socket, etc). But also many electronic items have filters in them that leak 1-2mA normally, so if you have enough items on a circuit it can be prone to such trips.

A good electrician should be able to verify the RCD and you cable, etc, is working correctly. That is the first step in doing any sort of corrective work.

If that checks out OK, then some can also do PAT testing of appliances to see if any are unusually leaky. If so you might decide to replace it.

But the other option that would normally be suggested on here would be to put the washing machine and related appliances on a separate RCD, so hopefully the total that is worrying close to the 15-30mA trip range is then split in two, and both are below the trip point.

How easy and cost-effective that is would depend on your CU, if it has the space and if it is recent enough that new compatible parts are still available.
[automerge]1598980551[/automerge]
Can you post a photo of your CU?

If it has any personal information on it then please blank that out, but what is of interest is the view of the MCB/RCD, not any labels.
[automerge]1598980881[/automerge]
I can't find the clear explanation I saw before, but this explains a bit about RCD:
Probably others will have a better site to link to.
[automerge]1598981695[/automerge]
Another point is many appliances are left powered on at the mains but in stand-by, in these cases they often have as much leakage as when fully operating. So if you are in an unfortunate position of total leakage close to RCD trip and can't afford to make the sort of changes needed to fully fix things to be reliable, you would have to actually turn the unused appliances off at the mains socket.

Obviously not things like the fridge though that need to be left on!
 
Last edited:
In many CU (consumer unit = fuse box) there are two types of breaker:
  • One or two RCD (residual current device) to trip on earth leakage, generally electric shock risk
  • 4-12 or so MCB (miniature circuit breaker) to trip on overload, typically a hard fault fire risk
So you will often find one RCD feeds several MCB, and you can turn of each circuit separately via the MCB, but if you do that to the RCD (e.g. the test button) then several circuits go off at once.


The unfortunate thing above the above arrangement is the RCD will trip if it sees somewhere between 15-30mA (1mA = 0.001A) going astray, and that can be due to various reasons that are a fault (bad cable insulation, water getting in to a junction box or socket, etc). But also many electronic items have filters in them that leak 1-2mA normally, so if you have enough items on a circuit it can be prone to such trips.

A good electrician should be able to verify the RCD and you cable, etc, is working correctly. That is the first step in doing any sort of corrective work.

If that checks out OK, then some can also do PAT testing of appliances to see if any are unusually leaky. If so you might decide to replace it.

But the other option that would normally be suggested on here would be to put the washing machine and related appliances on a separate RCD, so hopefully the total that is worrying close to the 15-30mA trip range is then split in two, and both are below the trip point.

How easy and cost-effective that is would depend on your CU, if it has the space and if it is recent enough that new compatible parts are still available.
[automerge]1598980551[/automerge]
Can you post a photo of your CU?

If it has any personal information on it then please blank that out, but what is of interest is the view of the MCB/RCD, not any labels.
[automerge]1598980881[/automerge]
I can't find the clear explanation I saw before, but this explains a bit about RCD:
Probably others will have a better site to link to.
[automerge]1598981695[/automerge]
Another point is many appliances are left powered on at the mains but in stand-by, in these cases they often have as much leakage as when fully operating. So if you are in an unfortunate position of total leakage close to RCD trip and can't afford to make the sort of changes needed to fully fix things to be reliable, you would have to actually turn the unused appliances off at the mains socket.

Obviously not things like the fridge though that need to be left on!
Hi, many thanks for the informative post.
I unplugged almost everything on the circuit with breaker that actually trips and I ran the machine and it completed with no trips. Of course, this doesn't really prove anything since the machine has completed successfully when everything has been plugged in (hence the intermittent nature of the tripping).

It really sounds as if the best thing to do is to forget about going back to Bosch and to get an electrician to look at it instead.

Here is picture of my unit. Sorry about the quality - the lighting is not very good at the moment. I will try to get a better picture tomorrow during the day. The machine and all the kitchen appliances apart from the boiler are covered the 32A circuit breaker on the far left (labelled A). The actual breaker (also 32A) that trips when the machine is on is the one next to it (second from left, labelled B). It is responsible for all the devices I listed in my earlier post:

IMG_20200831_122749050.jpg
 
I think it does. I have to pull it down (the red lever) and flick it back up again to get the power back.
Yeah, it does then.

Please confirm: when the tripping occurs, if you leave the tripped breaker B in the off position, and reset the RCD as you have just described, the power returns to the washing machine?
 
Yeah, it does then.

Please confirm: when the tripping occurs, if you leave the tripped breaker B in the off position, and reset the RCD as you have just described, the power returns to the washing machine?
I've never tried that before. I can try it the next time it trips and report back. I'll be using the machine again tomorrow, so if it trips, I will reset the RCD while leaving the tripped breaker off and I'll see what happens.
 
I've never tried that before. I can try it the next time it trips and report back. I'll be using the machine again tomorrow, so if it trips, I will reset the RCD while leaving the tripped breaker off and I'll see what happens.
Try this now: Leave breaker A on, switch off B, do you have power to the w/machine?
 

Reply to Washing machine intermittently trips RCD. Manufacturer declares machine fault-free and suggests faulty home electrics. What should I do? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
848
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi all, Was speaking to a family member recently, he told me his iron recently made a bang and flash as he plugged it in to the socket, and could...
Replies
14
Views
2K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock