OP
markusjames
DIY
- Reaction score
- 1
Is it the 3-phase supply cable from the distribution board to the dimmer rack?It's not clear what the OP is testing. Is it the 3-phase supply cable from the distribution board to the dimmer rack? Is the rack still connected to the cable? Are the outgoing lighting circuits still connected to the dimmers?
Again, what make and model of rack is it?
Yes!
Is the rack still connected to the cable?
Yes!
Are the outgoing lighting circuits still connected to the dimmers?
Yes!
Everything is still connected during Insulation testing in this particular dimmer rack. And only this rack failed the insulation test on 500v test with reading of 0.3Mohms.
I will start removing individual connection and run the test until I find the issue.