It's not clear what the OP is testing. Is it the 3-phase supply cable from the distribution board to the dimmer rack? Is the rack still connected to the cable? Are the outgoing lighting circuits still connected to the dimmers?

Again, what make and model of rack is it?
Is it the 3-phase supply cable from the distribution board to the dimmer rack?
Yes!
Is the rack still connected to the cable?
Yes!
Are the outgoing lighting circuits still connected to the dimmers?
Yes!

Everything is still connected during Insulation testing in this particular dimmer rack. And only this rack failed the insulation test on 500v test with reading of 0.3Mohms.
I will start removing individual connection and run the test until I find the issue.
 
At the moment, when you test N-E you are testing the supply cable, all the electronics in the rack, all the outgoing circuits, all the lighting fixtures powered by those circuits, literally the whole system at once. This is not a helpful test (unless it passes!)

Also, the manufacturers may not permit testing just N-E at 500V as this can put the test voltage across the output semiconductors. You must test in accordance with the manufacturers' instructions or you might damage the dimmers.

I can't add any more until you tell the model of the dimmer rack.
 
At the moment, when you test N-E you are testing the supply cable, all the electronics in the rack, all the outgoing circuits, all the lighting fixtures powered by those circuits, literally the whole system at once. This is not a helpful test (unless it passes!)

Also, the manufacturers may not permit testing just N-E at 500V as this can put the test voltage across the output semiconductors. You must test in accordance with the manufacturers' instructions or you might damage the dimmers.

I can't add any more until you tell the model of the dimmer rack.
We are using
C21 DIMMING SYSTEM
please refer to the photo.
This system supplied by 3 phase power.
 

Attachments

  • c21-dimming-rack.jpg
    71.7 KB · Views: 18
  • ec21-dimmersystem452-410.jpg
    48.5 KB · Views: 17

Reply to What are the implications of a failed Neutral - Earth insulation resistance test? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
642
Hi All, My colleague and I are currently doing PAT/ISITEE Testing, and we've hit a snag with a bit of equipment - we've got 19" Racks for our...
Replies
8
Views
514
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
715
During an insulation resistance test IR at an EICR I measured 0.0014 MegOhms from line to earth. When I disconnected the neutral from the neutral...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock