Kitchen RFC 2.5 T+E - IR=>200MOhms at 250VDC L&N to E but 0.34MOhms at 500VDC L&N to E.
I suspect damp/corrosion in sockets, what do you reckon?
All socket switches opened including SFCU to cooker hood, F/F, D/W and W/M.
 
Damp issues would be evident at 250v, as above surge protected lead or surge protection within an appliance. It could be an rcd spur or socket however these normally indicate low readings even at 250v.
 
Thanks for replies, I am trying to get an idea of actual readings for different accessories/appliances that can point me in the correct direction of what to hunt for. Today I was in a hoarders house with access to every socket impossible, got low readings LN&E, fridges/freezers always seem to have some leakage that will skew readings.
 

Reply to What are the possible causes of low IR readings at 500VDC? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
1K
I have been carrying out an EICR on a property and have come across this black tarry substance on 2 of the cables. I have seen the pitch oozing...
Replies
9
Views
4K
Looking for some guidance here. I'm currently shadowing a guy and we're testing a new extension on a school. 3 phase TNCS supply from the original...
Replies
6
Views
2K
Hi,guys went to do an EICR and when doing IR test I got L-E ON RFC like 0.02 MOHM and two lighting circuits L-E AND L-N the results were like 0,14...
Replies
6
Views
2K
What are the dangers of poor insulation resistance results (i.e <1Mohm) between neutral and earth? If all other tests are ok, what are the...
Replies
8
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock