Search the forum,

Discuss what causes loss of 24 VAC at the thermostat (and furnace) ? in the UK Electrical Forum area at ElectriciansForums.net

ktnwin

DIY
Reaction score
15
I replaced a very old thermostat, that still uses mercury for ON / OFF with a Honeywell digital thermostat.
The only issue with this old thermostat is it does not turn off the fan automatically after the gas furnace is OFF when room temperature reaches the setpoint.
The connection appears to be straightforward as there are 5 wires ( Red, Cyan, Green, Yellow and White )
These are at the thermostat (new and old) AND also at the furnace circuitry.
Red is the 24 Volts AC and Cyan is common. Green for the fan, Yellow for AC and White for heater.
After installation, the new thermostat does not turn on the furnace. It turns ON the fan even set to OFF.
I play around a few minutes, then nothing work, even the fan.
So I check the voltage between the RED and CYAN wires at the thermostat, which shows 24 Volts AC before, now shows 0 Volt. I go and check these same two wires at the furnace and also get 0 Volt,
Here are the pictures at the furnace
20210203_164759.jpg

The picture may show the top two terminals shorted but that is not the case if looking from top.
I did verify that there are 120V AC going the back of the transformer in this photo. There is NO fuse, no controller board.
What could cause the lost of 24V AC between these two RED and CYAN wires ?

I appreciate all help I could get.
Many thanks.
 
There is probably a thermal fuse or cutout within the transformer that has operated due to a short-circuit on the 24V side, or the transformer has failed. Disconnect all outgoing 24V wires from the terminals. If there is still 120V going in but no 24V coming out, disconnect the 120V input wires and check across the transformer terminals for continuity of the primary winding. It will probably show open-circuit, in which case you will need to either replace the transformer or disassemble it in case it is quicker and easier to replace the thermal fuse. Sometimes it is embedded within the winding and cannot be replaced, as the complete replacement transformer is unlikely to cost much.
 
Yes, I wonder actually whether something has been bypassed?
 
I replaced a very old thermostat, that still uses mercury for ON / OFF with a Honeywell digital thermostat.
The only issue with this old thermostat is it does not turn off the fan automatically after the gas furnace is OFF when room temperature reaches the setpoint.
The connection appears to be straightforward as there are 5 wires ( Red, Cyan, Green, Yellow and White )
These are at the thermostat (new and old) AND also at the furnace circuitry.
Red is the 24 Volts AC and Cyan is common. Green for the fan, Yellow for AC and White for heater.
After installation, the new thermostat does not turn on the furnace. It turns ON the fan even set to OFF.
I play around a few minutes, then nothing work, even the fan.
So I check the voltage between the RED and CYAN wires at the thermostat, which shows 24 Volts AC before, now shows 0 Volt. I go and check these same two wires at the furnace and also get 0 Volt,
Here are the pictures at the furnace
View attachment 64398
The picture may show the top two terminals shorted but that is not the case if looking from top.
I did verify that there are 120V AC going the back of the transformer in this photo. There is NO fuse, no controller board.
What could cause the lost of 24V AC between these two RED and CYAN wires ?

I appreciate all help I could get.
Many thanks.
I replaced a very old thermostat, that still uses mercury for ON / OFF with a Honeywell digital thermostat.
The only issue with this old thermostat is it does not turn off the fan automatically after the gas furnace is OFF when room temperature reaches the setpoint.
The connection appears to be straightforward as there are 5 wires ( Red, Cyan, Green, Yellow and White )
These are at the thermostat (new and old) AND also at the furnace circuitry.
Red is the 24 Volts AC and Cyan is common. Green for the fan, Yellow for AC and White for heater.
After installation, the new thermostat does not turn on the furnace. It turns ON the fan even set to OFF.
I play around a few minutes, then nothing work, even the fan.
So I check the voltage between the RED and CYAN wires at the thermostat, which shows 24 Volts AC before, now shows 0 Volt. I go and check these same two wires at the furnace and also get 0 Volt,
Here are the pictures at the furnace
View attachment 64398
The picture may show the top two terminals shorted but that is not the case if looking from top.
I did verify that there are 120V AC going the back of the transformer in this photo. There is NO fuse, no controller board.
What could cause the lost of 24V AC between these two RED and CYAN wires ?

I appreciate all help I could get.
Many thanks.
I have to agree with @telectrix and I’ve been through this before, the transformer has NO protection on the secondary side of your transformer and somehow when you was wiring it up obviously the 24vac live wire event to ground or made contact with the neutral. The transformer is no good no more. If you replace it install a inline fuse on the secondary side of the transformer
 
First, I verified that the new thermostat setting was for electric, supposed to be gas. My fault here. That was why it does not control the furnace properly. Anyway, I lost 24 VAC. Today, I remove the wires going into the two top terminals at the transformer, shown by yellow arrows, RED on the left, and the 3 wires taped together with blue tape on the right, the large size black wire cannot be removed.
20210204_114921B.jpg


I opened the transformer and yes, the two wires from the secondary are soldered to these two terminals.
I measured the resistance between these two terminals and got approximately 5 Ohms. So the secondary is NOT opened, NOT shorted. I have no idea whether 5 Ohms is correct or not. Any advise with this new info I like to be sure it is bad before replacing it.
 
check for 24V ac on the secondary with those wires disconnected.
 
The secondary winding is unlikely to fail. As I suggested, test the primary, as that is wound with much finer wire and is the more likely to fail open, and also if there is a thermal fuse that will be in the primary.
 
Still trying to remove the transformer to access the primary.
A second thought: 5 Ohms for secondary is too low as it means 24V / 5 = 4.8A current going thru it. These transformer uses 3A fuse if they have one.
I will order a new one anyway, it only costs around 20+$. Will make sure to add a fuse.
 
DC resistance, measured with a meter, is much lower than AC "resistance".
Thanks, I will double check my understanding with one of the 3 working 18 VAC transformers. These are for door bell, light for house number in front of garage, and one for ???
Just measure the secondary of these 3 18 VAC transformers, all measure 6 Ohms. From my understanding, 5 and 6 Ohms are normal for secondary.
Will find out more after removing the transformer. I am very curious to know. This transformer has a switch to cut off power going to it, very convenient to work with.
 
Last edited:
Eureka, I finally remove the transformer. Carefully mark where its black and white wires were connected with black tape and white tape on the wire nuts. These are simply hot and neutral wires in any electrical box.
20210204_142534.jpg


The primary winding is indeed OPEN. A simple test by connecting it to 120 VAC results in 0 Volt at the secondary output lines. I am going to order a new transformer and 3A fuses now.
Question: is the fuse to be inline with the primary or secondary ? My guess is secondary but I like to be absolutely sure from expert input.
 
fuse should be on the primary side, but there's nothing to stop you adding a fuse to the secondary.
 
Eureka, I finally remove the transformer. Carefully mark where its black and white wires were connected with black tape and white tape on the wire nuts. These are simply hot and neutral wires in any electrical box.
View attachment 64434

The primary winding is indeed OPEN. A simple test by connecting it to 120 VAC results in 0 Volt at the secondary output lines. I am going to order a new transformer and 3A fuses now.
Question: is the fuse to be inline with the primary or secondary ? My guess is secondary but I like to be absolutely sure from expert input.
I’ve had a relay blow on my unit and with no secondary fuse it fried all the wires in the control box and I didn’t even know it until I started smelling smoke, I looked and my kitchen was full of smoke. Had to replace the unit. That’s why I tell you to add a secondary fuse. If mine would have had a secondary fuse my unit could have saved.
 
fuse should be on the primary side, but there's nothing to stop you adding a fuse to the secondary.
Don't agree. The Tx comes with primary side protection in the form of the thermal fuse.
The fuse in this case is required because it connects to wiring outside the boiler, which is not under the control of the manufacturer, so should be fitted to the secondary.
 
I will add the fuse to the secondary then as it seems to make sense to me. When the 24 VAC line get shorted somehow (by accident), then the fuse inline on the secondary will blow and the two wires of the secondary are no longer connected, the primary remains intact in this case.
If I know the max amp rating of the primary, I can add one inline here too (1, 2 or 3 Amp ???). This 24 Volt transformer is connected to a 15 Amp circuit along with 3 other 18 Volt transformers. These four transformer can hardly draw 15 amps on 120 Volt line.
The fuse kit I bought has 5 fuses for each amp rating, plenty of fuse holders too.
(1A 2A 3A 4A 5A 7.5A 10A 15A 20A 25A 30A 35A 40A)
The transformer and fuses will be delivered tomorrow, I can't wait to get the heater to work again.
I will be very careful this time, connect 24 volts to the thermostat (only 2 wires), then change system (heat, cold), FAN settings to verify that the 24 Volts appear at the other 3 wires correctly based on the settings.
Only when the thermostat behaves properly, I will connect the other 3 wires.
 
I will add the fuse to the secondary then as it seems to make sense to me. When the 24 VAC line get shorted somehow (by accident), then the fuse inline on the secondary will blow and the two wires of the secondary are no longer connected, the primary remains intact in this case.
If I know the max amp rating of the primary, I can add one inline here too (1, 2 or 3 Amp ???). This 24 Volt transformer is connected to a 15 Amp circuit along with 3 other 18 Volt transformers. These four transformer can hardly draw 15 amps on 120 Volt line.
The fuse kit I bought has 5 fuses for each amp rating, plenty of fuse holders too.
(1A 2A 3A 4A 5A 7.5A 10A 15A 20A 25A 30A 35A 40A)
If I was you I would go with the 3 amp and remember we are not worried about overcurrent, we are worried a short circuit.
 
If I was you I would go with the 3 amp and remember we are not worried about overcurrent, we are worried a short circuit.
Correct, these transformers cannot draw up to 15A. I will also add a 3A fuse to the primary. So, two fuses for this transformer to protect it. It is very annoying when it is toasted.
 
Correct, these transformers cannot draw up to 15A. I will also add a 3A fuse to the primary. So, two fuses for this transformer to protect it. It is very annoying when it is toasted.

Correct, these transformers cannot draw up to 15A. I will also add a 3A fuse to the primary. So, two fuses for this transformer to protect it. It is very annoying when it is toasted.

The new transformer cannot fit in the place where the old one is. So, I left the old one at the same place after disconnecting it from the 120V input, its outputs also disconnected. The new one is installed on the side of a metal switch box (where other transformers are), I ensure that its hot is only hot when the switch is ON. The 24VAC output goes thru a cable with its 2 wires connected to where the old transformer outputs are connected to. The hot 24V also has a 3A fuse inline. I have no room to add fuse for its 120V input.
Turn ON the breaker and test, my new Honeywell thermostat did control the heat as expected. But the fan is ONLY on if I set it to ON. It does not turn ON in AUTO mode even if the heat is ON (a new post will be created for this).
For now, this topic ends here.
 

Reply to what causes loss of 24 VAC at the thermostat (and furnace) ? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

First time DIY post here…. My wife and I bought an old, run down 70’s lake trailer and ran into an AC wiring issue. Our thermostat is wired...
Replies
3
Views
741
Hello everyone. Budding DIY enthusiast fascinated with how things work - and, to a lesser degree, fixing things that are not working. I suppose my...
Replies
0
Views
1K
For the past few years, I have used a hydronic system (outdoor wood boiler) with both high and low temp working simultaneously. The low temp...
Replies
6
Views
817
Hi, have an old bathroom fan. Which has two wires the black and red (line and neutral). The fan has no isolator switch and was powered when the...
Replies
3
Views
712
Hi, I installed 6 recessed lights in my living room. I’m now up to the wiring part of the project. There is an outlet in the room that is...
Replies
1
Views
502

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock