Discuss What Reg states you cant have 2 RFC's in one fuse? in the Australia area at ElectriciansForums.net

L

lawrence0117

Hey guys, just out of interest, just completed a job for a customer but whilst i was in the board(old 5 way wylex) i noticed both ring circuits on one 32a fuse (space saving?)and cant rememeber off the top of my head and wondered if one of you lovely people knew the actual reg that states its a possible no no? i know its bad practise but just wondered if there was an actual reg?
Cheers,
lawman
 
can't think of a reg apart from the one about separation of circuits and discrimination betwixt them (sorry no regs to hand)

As a safety thing can't think of a bad point apart from premature ..... tripping. As in too many things plugged in expecting the capacity afforded by two RFC's
 
If they are both installed separately in accordance with appendix 15 and 433.1.5 then the only issue is with regard to section 314 (Division of installation).
I suspect though that it is likely that 433.1 will not be complied with as it is likely that "Ib" will possibly exceed "In" in some circumstances.
 
Ive been looking through regs and scratching my head! Thats what i thought, from a safety point of view the only bad point might be its gonna trip because they may overload it in the future? well, i pointed it out to them but they said they havent ever had any trouble so mehh!!

I like what your saying widdler 314 looks good, just found it in regs and 433.1!

cheers for your quick knowledge!
 
Last edited by a moderator:
Definition of a 'circuit' - An assembly of electrical equipment supplied from the same origin and protected against overcurrent by the same protective device(s).

Two ring finals in one MCB would be one circuit, not two circuits in one MCB. Pretty crap though.
 
Last edited by a moderator:
Definitions, rfc = a final circuit arranged in the form of a ring and connected to a single point of supply.

No mention of 2 rfc on the same point of supply. Erm good question.

Only other thing from top of my head is appendix 15, "An unfused spur may be connected to the origin of the circuit in the distribution board". It says "an" not "another ring".
 
Have a look at the first line of reg 537.2.1.1 and now member the description in definitions of a "ring final 'circuit'.

Imho a rfc is one circuit and two should not be placed on the same mcb/fuse.
 
In that case, two times two loops of cable connected together in a single MCB isn't a ring final circuit, merely two times two loops of cable in a single MCB and by definition, a circuit.

I'm not arguing a case for this cack design of a circuit, just struggling to argue against it.
 
Last edited by a moderator:
Doh, I've written a long post and lost it in cyber space. Not doing it again, its to late.

Gary I agree with you. In the end there is no reg set in stone against this but would anyone of us do it? No.

Can anybody show us a reg?
 

Reply to What Reg states you cant have 2 RFC's in one fuse? in the Australia area at ElectriciansForums.net

Similar Threads

Doing one more of the flood of EICR today on a rented property before a tenant change, but ran into a slightly interesting case so would...
Replies
71
Views
13K
C
Hi All, First off.. I'm NOT an electrician and am not about to commence DIY electrical work! Just looking to get clued up before calling a...
Replies
2
Views
4K
Meggerman
M
1
My mind is boggling at the moment as I am in the process of quoting to install a cooker, quite a bloomin large one in my opinion but just...
Replies
9
Views
1K
alarm man
A
P
Now - up to about ten min's ago - i thought I had this install sussed- I'm a bit tired so I may just be misunderstanding some of the posts on this...
Replies
13
Views
4K
P
Got a couple of Q's that any ideas on would be appreciated. Lady down road has 16th Ed CU fitted by her ex husband just before he left her. It's...
Replies
13
Views
2K
Poptasticdave
P

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock