Search the forum,

Discuss Whats this mean on a rcd test in the UK Electrical Forum area at ElectriciansForums.net

I would like to add my morsel.

When I did my C&G course on initial testing & inspection, I was taught to use an MFT with plug & lead at a socket to conduct RCD testing. I can see when there perhaps is no other option to test at the RCD terminals, i.e. RCBO protected radial circuit with just FCU at the end. Electricity at Work Regs does permit working live, but only if ‘unreasonable in all circumstances to be dead’ etc.

I have looked at several references on how to carry out the functional test of an RCD.

GN3 states; ‘the test is made on the load side of the RCD between line conductor of the protected circuit and associated cpc’.

OSG goes on to add; ‘as near as practicable to its point of installation’.

I find that somewhat ambiguous. If I was trying to describe the test being conducted at the RCD terminals only, I would not use the phrase ‘load side of the RCD between line conductor of the protected circuit and associated cpc, and as near as practicable to its point of installation’.
I would have written something like ‘on the load side terminals of the device being tested and not on the circuit being protected’. But that’s my opinion.

Unfortunately neither GN3 nor OSG have a pretty set of diagrams (unlike most other tests) to reinforce what they are actually describing.

BEAMA RCD Handbook; All tests must be performed with all loads disconnected, making use of an appropriate calibrated test instrument connected as close to the RCD as possible for convenience.

Advanced Electrical Installation Work publication (by Trevor Linsley); ‘…using standard lead supplied with MFT, disconnect all loads and plug in test lead into socket at the centre of the ring (i.e. socket at the furthest point from the source of supply).

I have spent some time web engine searching to find anything to suggest that the test ‘MUST’ be carried out on the RCD terminals ‘ONLY’, with a negative result.

I’ve emailed some of the RCD manufacturers, putting forward both sides of the argument (citing, poor IR, other leakage currents and possibly cable capacitance reasons for not carrying out test at socket etc), some of them responded;

MK: Unfortunately we are unable to comment on site specific testing of any devices including RCDs; however we would advise that all testing must be carried out strictly in accordance with the requirements of BS7671 and associated guidance notes.

Hager: The correct way to test an rccb is at the terminals with the load disconnected in accordance with the on site guide.

Wylex: The test should be carried out as near as practicable to its point of installation. This may vary from install to install and it may be that a test using a plug in lead at the first socket is that nearest practicable point, just depends upon the install and any accessibility issues that may exist.

Then others;

Elecsa: The issue here is being able to test the RCD in a safe manner. Whilst the OSG and GN3 state “load side of the RCD with loads disconnected” which suggests purely testing the RCD at the board, it is quite an acceptable option to test the RCD by plugging the tester into a socket as long as your tester has that facility to allow you to do that.

Electrical Safety First: Usually we would refer you to the (scheme helpline), but I have scanned in this page (attached in .pdf format) from our “snags and solutions” guide, which will hopefully be helpful. This refers to the NICEIC booklet part 3 Inspection & testing; Snag 49 RCD testing – when current using equipment is connected. Answer: disconnect equipment, measure at any convenient point in the circuit, such as socket outlet. There is also a diagram that shows test being done at the RCD terminals with circuit still connected, but loads disconnected.

I then asked my training establishment: 'It does not matter where on the circuit you carry out the test as the tester uses a set amount of current i.e. for a 30 mA rcd at 1x the tester will use 30 mA thus the resistance of the circuit cable is compensated for. If the circuit resistance was a factor so would the Ze value be. It is convenient and safer to carry out the test at a convenient socket.' (There is a longer response from them, which I haven’t included here).

Kewtech: Both are correct. You have to look at practicality and accessibility. What happens if you test at a socket and the RCD does not trip due to an earth fault and you then go to the board and test the RCD and it trips? You have proved the RCD at the board as opposed to the socket.

Lastly I spoke to my MFT manufacturer (Megger). Who said; neither is the wrong way to carry out the test, but it would be preferable to test on the circuit being tested. Poor I/R should have already been tested and investigated, earth leakage should not be present (as loads disconnect) & the circuit would have to be extremely long for cable capacitance to have an effect (also loads disconnect) (not verbatim conversation). Also said ‘we are aware of an RCBO – MEM MR30 – which will not function test with the tester at its terminals, but will when tested on the circuit being protected (I can provide the citation if required).
 
I'm suprised that MK don't feel able to advise on the safe use of their products. Hopefully they themselves know how to test an RCD.

I agree that it should not matter where on the circuit you test as far as test validity or performance are concerned, unless the circuit parameters are exceptional. I would avoid disconnecting conductors unless essential, and I know of RCDs that can't be tested from the terminal screw heads as the outgoing cables themselves pass through the transformer core. Other than that I'd go with the safest / most convenient location. One advantage of testing at the device in a CU is that the test path can be from load L to supply N, avoiding reliance on the CPC. At a socket outlet, the test must use the CPC. as the supply side is inaccessible. OTOH one is then working with higher PFC on the test leads and greater chance of arc flash or shock injury in the event of damage.

Whether the circuit is connected or not will only make a significant difference if the cable runs are extreme or the IR very poor. 1 megohm L-E only contributes 0.23mA of resistive leakage and 100m of 2.5 T+E another 0.8mA of capacitive leakage (at 110pF/m), possibly a bit more if run in contact with earthed structure. Normal domestic circuits in good condition should not materially affect any but the most borderline RCD tests. Likewise the effect of r2 should be negligible if continuity has already been proven.
 
Good work Mid. So no definitive answer then! As near as possible to terminals seems to be the main guidance gleaned from that lot.
 
I think consideration should first be given as to why the RCD test is being conducted.
Is the purpose of an RCD test, to prove that the RCD operates, or that it provides the intended protection?
All very well proving an RCD operates at the board, but not much use in proving that the RCD provides protection for circuits of a location containing a bath or shower, socket-outlets, equipment used outdoors or cables concealed in walls.
 
The other side of the argument, sorry discussion, is that having completed all the other tests, when testing the RCD it is just a function test of the device itself, which could be carried out at it's terminals. That said, you have to consider conducting that test inside a live CU. We are all skilled persons (and grown up enough to know how careful to be), but I don't know why take the risk, when it can be carried out otherwise? The suggestion to dismantle bus bars or disconnect circuit conductors to carry out a device test only doesn't seem necessary, to me anyway. Unnecessary disturbance of a CU. Perhaps we shall see further debate shortly?
 
I think consideration should first be given as to why the RCD test is being conducted.
Is the purpose of an RCD test, to prove that the RCD operates, or that it provides the intended protection?
All very well proving an RCD operates at the board, but not much use in proving that the RCD provides protection for circuits of a location containing a bath or shower, socket-outlets, equipment used outdoors or cables concealed in walls.

Nonsense, if it works it works. The outgoing wiring will not make it trip slower or be less sensitive if it has passed the other tests, what it can do is make it trip faster.
 

Reply to Whats this mean on a rcd test in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
406
Evening everyone… I’ve attached pictures for your leisure.. so basically the customer does not have any RCD protection.. 3036 fuseboard is in...
Replies
9
Views
448
Hello. I will be buying new apartment to live. But electrical plugs are older. Not the newest. And my question. It will be fine to plug pc in this...
Replies
4
Views
436
Hi, I was looking at my dishwasher and it has this metal plate with these markings. I am confused about the meaning of "10/16A" - does that...
Replies
4
Views
280
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
874

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock