Discuss When does 3 phase supply become 230V in domestic consumer unit? in the UK Electrical Forum area at ElectriciansForums.net

Which raises an important question - which metered supply is the EVCP to be connected to?
I don't think the owner would be too fussed which meter it comes off, but I would certainlt discuss it before making a decision.
Is the job for the property owner? If so, you could always install a small single phase CU as a 'Landlord's supply'. Doesn't seem to be one, from the photo.
Yes, its for the owner. What do you mean 'landlords supply'? Actually, I may not be understanding your question properly. It is for the owner, but it will be used by the customers.
Any spare ways on the MG board, just above the intake? If possible I would seriously consider fitting a 3ph EVCP if the facility is there for future expansion and rapid charging.

Three phase is easy enough to work on you just need to remember the full safe isolation process which has a few more steps than single phase.

3 Phase installations test to confirm that there is no voltage between:

  • L1 and L2
  • L1 and L3
  • L1 and Neutral
  • L1 and Earth
  • L2 and L3
  • L2 and Neutral
  • L2 and Earth
  • L3 and Neutral
  • L3 and Earth
  • Neutral and Earth

When energised you should see voltage between earth and neutral:

L1 - 230V
L2 - 230V
L3 - 230V

Line to line you should see:

L1 - L2 - 400V
L1 - L3 - 400V
L2 - L3 - 400V

To get single phase from three phase all you do is connect to one of the phases and use the neutral.
I do understand safe isolation of 3 phase, but when you guys start talking about 'out of phase, star and delta etc' I am lost. If I don't understand something as basic as that I don't think I should be adding to the 3 phase part of it. However, it does sound as though a 3 phase EVCP would be a better option for the owner. I'll make him aware of that so he can look elsewhere if he chooses.
 
Generally it looks a neat and well done installation.

The 300mA RCD for agriculture areas (special area for fire protection, don't have regs to hand) is not needed for your EV supply, but if for any reason you are taking the power from one of those unused fused-switches you need at least a 30mA A-type RCD as well so it is selective with the up-fornt RCD (I am assuming here it is a delay type, it should be...). But check if the EV model need a B-type for DC leaks.
 
Who is paying for the use of the EV charger?

I ask as there are lots of meters, and it is not obvious who pays for what. It is probably the site owner who pays the main 3-phase meter bill on the right, but after that?

Even if it is that person, if there is a spare single meter & fused-switch that can be used they might like the visibility of the EV use to be shown.
The owner would be paying. The EVCP would be for use by the customers.
Looking at the spare meters, they look like a good choice! if indeed they are spare, and the cables are not hidden behind. I wish I'd taken a peek.
 
Generally it looks a neat and well done installation.

The 300mA RCD for agriculture areas (special area for fire protection, don't have regs to hand) is not needed for your EV supply, but if for any reason you are taking the power from one of those unused fused-switches you need at least a 30mA A-type RCD as well so it is selective with the up-fornt RCD (I am assuming here it is a delay type, it should be...). But check if the EV model need a B-type for DC leaks.
Yep, happy with all the RCD requirements. That's one thing I do understand. More so after your 'blinding' experiment. ?
 
The owner would be paying. The EVCP would be for use by the customers.
Looking at the spare meters, they look like a good choice! if indeed they are spare, and the cables are not hidden behind. I wish I'd taken a peek.
Check with the owner about the meter use in case not all are wired up.

You probably have space to the left to add another meter (if owner wants one), wiring is much as they are done already and probably a spare way or two on the existing Henley blocks for putting in the new L & N tails. Ideally try to get the same makes & models so it all looks consistent and works in the same sort of way.

Just be very sure you don't use two of the L blocks or you will see 400V! As explained above L-L is nominally 400V and L-N nominally 230V so it is which pair of cables you use.

Edit to add: The tails look colour coded with tape, but the N blocks are obvious as there are two cascaded to have enough holes to fill (oh-err) as 6 single phase means 2 per phase and 6 per neutral block. Might be worth checking with a clamp meter or looking at loads to select a phase that is lower loaded to keep the 3 in a better balance when EV on.
 
Last edited:
Check with the owner about the meter use in case not all are wired up.

You probably have space to the left to add another meter (if owner wants one), wiring is much as they are done already and probably a spare way or two on the existing Henley blocks for putting in the new L & N tails. Ideally try to get the same makes & models so it all looks consistent and works in the same sort of way.

Just be very sure you don't use two of the L blocks or you will see 400V! As explained above L-L is nominally 400V and L-N nominally 230V so it is which pair of cables you use.

Edit to add: The tails look colour coded with tape, but the N blocks are obvious as there are two cascaded to have enough holes to fill (oh-err) as 6 single phase means 2 per phase and 6 per neutral block. Might be worth checking with a clamp meter or looking at loads to select a phase that is lower loaded to keep the 3 in a better balance when EV on.
Thanks PC. That all makes sense. Yes, it is obvious which is the neutral, plus I can test to make certain.
 
A 'Landlords supply' is separate from all the tenants, who have their own meters. It is generally used for essential circuits in multi tenanted buildings like stair case lighting, outside lighting or other maintenance/cleaning facilities, available. Maybe even fire alarm supply or emergency lighting.

I don't think you'd have much problem picking up for a single phase DB.
That MG board might be interesting, Solar involved but it has a mains 3 phase supply, by the looks.

Remember, even if it's for the tenants, one of them won't want to pay for it, if it's for all.
 
Last edited:
But at which exact point does it change from 400v to 230V? How can it decrease in voltage without a transformer? I think this last question is also the answer to your question Julie ?

ps.. I'm assuming the 3 phase CU in the picture below is fed from the switched fuse (A) (single phase). How can it be a 3 phase board? Is it a 3 phase board? It looks like it only has a 2 pole isolation switch. I'm guessing it's actually single phase?

View attachment 90321

Wow if you honestly don’t know how to get single phase from a 3 phase supply you shouldn’t be let loose near electrics

btw the isolator in the db is only 2 pole so my gues would be that it is a 3 phase db with a single phase conversion kit
 

Reply to When does 3 phase supply become 230V in domestic consumer unit? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Recently started a retrofit where the 3 phase dB has been fitted with bushes through the galv trunking. The single phase supplies outgoing have...
Replies
1
Views
263
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
794
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
311
Can a domestic consumer unit feed another consumer unit, via the Main Switch. Details are: domestic property with 100A single phase supply...
Replies
9
Views
477
Good morning, So I’m working on an existing 3 phase solar system and the customer wants a way to use the huge mass of exported solar on their...
Replies
3
Views
990

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock