Where to start.

Discuss Where to start. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
53
Been out to a family member that has just brought a new property.

He would like a few new sockets the usual. Open the cupboard under the stairs to find this.

epatu7e7.jpg


anu7y2up.jpg


ru9u3yvu.jpg


7a8y7ete.jpg


All earthed metal conduit. A real piece of workmanship just seems a shame to take it all out. Would be nice to keep some of it but where to start!

The lack of rcd protection being the main problem for any additions.

What would you guys do?
I was considering a second board and running new circuits out or possibly using the conduit to pull new cables through and then floor boards up and new rings?

All advise welcome!
 
If it were me then I,d be making some of the radials into rings,flexi conduit and add earth for the under floor bit,as for rcd I,d just put one up front if I were that bothered.as others have said that install will outlast a lot of the modern crap.
 
The owner actually quite like it.

Would have been nice if the guy that fitted it labelled it up though.

Have spent all morning with this

7ymabavu.jpg


And it new friend:

be4u2atu.jpg


For the old sockets with 4.5A fuse wires.

Im considering running 16a radials to each room through the old conduit and adding new sockets from the original position.

Hopefully saving the walls as much as possible then its just floors up.

The lights im going to test, They seem to be live looped in at the switch,

u5etanun.jpg


And the neutrals and the switch line at the light itself.

Starting to think din rails in the old case with an rcd up front for the sockets

Then putting the lights on mcbs (no rcd) as its earthed metal conduit.

One question

I have seen small metal bars fitted in old imperial size light fittings so that new switches can be fitted (due to position of the patress screws)

Does anybody know what these are called or where i might source them?

As replacing the old solid ones would be a nightmare and involve smashing the wall to bits.

Can see this job being a real labour of love!
 
Last edited:
There’s got to be a way to reuse a lot of that.
Shanky’s suggestion of a metal clad board sits well with me but I’d go for SPSN RCBO’s. Not a cheap solution I know but how much time is it going to take to rip it all out and start again?

Like anything, money will govern what gets done.

I’ve got to say, I love how that neutral bar has been done.
 
If everything is in steel conduit, wiring in good condition and tests out well.....why not change all the sockets to RCD version ?....and add a 17th board for any new stuff, of course.
 
If everything is in steel conduit, wiring in good condition and tests out well.....why not change all the sockets to RCD version ?....and add a 17th board for any new stuff, of course.
crap idea. 1. cost. 2. cables to sockets still not RCD protected. my solution would be to fit a RCD/MCB sub-main for the new work and leave the existing well alone ( except for getting rid of any neutral fusing)
 
crap idea. 1. cost. 2. cables to sockets still not RCD protected. my solution would be to fit a RCD/MCB sub-main for the new work and leave the existing well alone ( except for getting rid of any neutral fusing)

Can't remember such bullsh0t from you before.....20odd rcd sockets ain't gonna break anyone.....and as regards the cable protection...time you came out of hibernation, tel...:8:that lager must have gone to your head, mate.
 
Can't remember such bullsh0t from you before.....20odd rcd sockets ain't gonna break anyone.....and as regards the cable protection...time you came out of hibernation, tel...:8:that lager must have gone to your head, mate.

Say what ?
If I was sorting out this job I would much rather have £300 to spend on materials in the distribution cupboard than spend the same amount on littering butt ugly RCD sockets about the place and call it a job.
 
Say what ?
If I was sorting out this job I would much rather have £300 to spend on materials in the distribution cupboard than spend the same amount on littering butt ugly RCD sockets about the place and call it a job.

Say what you want......I thought he was after options.
 
I quite like them. The gist I think was to save the gear in the cupboard. I think it was a valid suggestion

I agree such a rare thing (these days) should be preserved if possible. But looking at horrifically thick white plastic tat with coloured buttons sat on the walls every day as opposed to glancing a plastic CU every once in a while ? I know what I would want for my own house.

I reckon a custom job could be the way forward to strike a balance between regs compliance and deference for the skills of a former electrician. I say that the MEM cabinet could be stripped out and adapted to house din rails (as hinted at by the OP) and allow the alterations.
Would be a complete labour of love mind you.
 
I agree such a rare thing (these days) should be preserved if possible. But looking at horrifically thick white plastic tat with coloured buttons sat on the walls every day as opposed to glancing a plastic CU every once in a while ? I know what I would want for my own house.

I reckon a custom job could be the way forward to strike a balance between regs compliance and deference for the skills of a former electrician. I say that the MEM cabinet could be stripped out and adapted to house din rails (as hinted at by the OP) and allow the alterations.
Would be a complete labour of love mind you.

Options and opinions, then. You get what you pay for.
 
In ripping it apart and rebuilding it with MCBs etc you are pretty much building your own DB for which I would imagine you'll have to deal with CE marking and lots of statutory regulations.

My earlier suggestion of fitting an enclosure with main switch and 2 RCDs to feed each row of fuses would be much simpler.
It wouldn't take much to chop that neutral bar in two.
 
In ripping it apart and rebuilding it with MCBs etc you are pretty much building your own DB for which I would imagine you'll have to deal with CE marking and lots of statutory regulations.

My earlier suggestion of fitting an enclosure with main switch and 2 RCDs to feed each row of fuses would be much simpler.
It wouldn't take much to chop that neutral bar in two.

I'm not sure you would have to justify such a build to any particular standard, but it would certainly be a PITA ... lol
 

Reply to Where to start. in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top