Discuss Where to start. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
53
Been out to a family member that has just brought a new property.

He would like a few new sockets the usual. Open the cupboard under the stairs to find this.

epatu7e7.jpg


anu7y2up.jpg


ru9u3yvu.jpg


7a8y7ete.jpg


All earthed metal conduit. A real piece of workmanship just seems a shame to take it all out. Would be nice to keep some of it but where to start!

The lack of rcd protection being the main problem for any additions.

What would you guys do?
I was considering a second board and running new circuits out or possibly using the conduit to pull new cables through and then floor boards up and new rings?

All advise welcome!
 
The thing that bothers me most about replacing it is there really is nothing wrong with it ( apart from not meeting current regulations) and would out last the cheap Chinese tat that replaces it!
 
If it were me then I,d be making some of the radials into rings,flexi conduit and add earth for the under floor bit,as for rcd I,d just put one up front if I were that bothered.as others have said that install will outlast a lot of the modern crap.
 
Lovely. Proper gear. As said will outlast the latest plastic cobblers.

i expect they will not want you to leave it though, as cupboard space will be taken up.
 
The owner actually quite like it.

Would have been nice if the guy that fitted it labelled it up though.

Have spent all morning with this

7ymabavu.jpg


And it new friend:

be4u2atu.jpg


For the old sockets with 4.5A fuse wires.

Im considering running 16a radials to each room through the old conduit and adding new sockets from the original position.

Hopefully saving the walls as much as possible then its just floors up.

The lights im going to test, They seem to be live looped in at the switch,

u5etanun.jpg


And the neutrals and the switch line at the light itself.

Starting to think din rails in the old case with an rcd up front for the sockets

Then putting the lights on mcbs (no rcd) as its earthed metal conduit.

One question

I have seen small metal bars fitted in old imperial size light fittings so that new switches can be fitted (due to position of the patress screws)

Does anybody know what these are called or where i might source them?

As replacing the old solid ones would be a nightmare and involve smashing the wall to bits.

Can see this job being a real labour of love!
 
Last edited:
There’s got to be a way to reuse a lot of that.
Shanky’s suggestion of a metal clad board sits well with me but I’d go for SPSN RCBO’s. Not a cheap solution I know but how much time is it going to take to rip it all out and start again?

Like anything, money will govern what gets done.

I’ve got to say, I love how that neutral bar has been done.
 
If everything is in steel conduit, wiring in good condition and tests out well.....why not change all the sockets to RCD version ?....and add a 17th board for any new stuff, of course.
 
If everything is in steel conduit, wiring in good condition and tests out well.....why not change all the sockets to RCD version ?....and add a 17th board for any new stuff, of course.
crap idea. 1. cost. 2. cables to sockets still not RCD protected. my solution would be to fit a RCD/MCB sub-main for the new work and leave the existing well alone ( except for getting rid of any neutral fusing)
 
crap idea. 1. cost. 2. cables to sockets still not RCD protected. my solution would be to fit a RCD/MCB sub-main for the new work and leave the existing well alone ( except for getting rid of any neutral fusing)
the cables dont need to be rcd protected if they are in metalic containement and im sure only sockets exspected to be used outdoors need rcd
 
You could seperate the two rows of fuses and supply each one through external RCDs,
You'd just need to get a six way enclosure with main switch and two RCDs.
Fit it in there in place of that main switch and away you go.
 
crap idea. 1. cost. 2. cables to sockets still not RCD protected. my solution would be to fit a RCD/MCB sub-main for the new work and leave the existing well alone ( except for getting rid of any neutral fusing)

Can't remember such bullsh0t from you before.....20odd rcd sockets ain't gonna break anyone.....and as regards the cable protection...time you came out of hibernation, tel...:8:that lager must have gone to your head, mate.
 
Can't remember such bullsh0t from you before.....20odd rcd sockets ain't gonna break anyone.....and as regards the cable protection...time you came out of hibernation, tel...:8:that lager must have gone to your head, mate.

Say what ?
If I was sorting out this job I would much rather have £300 to spend on materials in the distribution cupboard than spend the same amount on littering butt ugly RCD sockets about the place and call it a job.
 
Say what ?
If I was sorting out this job I would much rather have £300 to spend on materials in the distribution cupboard than spend the same amount on littering butt ugly RCD sockets about the place and call it a job.

Say what you want......I thought he was after options.
 
I quite like them. The gist I think was to save the gear in the cupboard. I think it was a valid suggestion

I agree such a rare thing (these days) should be preserved if possible. But looking at horrifically thick white plastic tat with coloured buttons sat on the walls every day as opposed to glancing a plastic CU every once in a while ? I know what I would want for my own house.

I reckon a custom job could be the way forward to strike a balance between regs compliance and deference for the skills of a former electrician. I say that the MEM cabinet could be stripped out and adapted to house din rails (as hinted at by the OP) and allow the alterations.
Would be a complete labour of love mind you.
 
I agree such a rare thing (these days) should be preserved if possible. But looking at horrifically thick white plastic tat with coloured buttons sat on the walls every day as opposed to glancing a plastic CU every once in a while ? I know what I would want for my own house.

I reckon a custom job could be the way forward to strike a balance between regs compliance and deference for the skills of a former electrician. I say that the MEM cabinet could be stripped out and adapted to house din rails (as hinted at by the OP) and allow the alterations.
Would be a complete labour of love mind you.

Options and opinions, then. You get what you pay for.
 
In ripping it apart and rebuilding it with MCBs etc you are pretty much building your own DB for which I would imagine you'll have to deal with CE marking and lots of statutory regulations.

My earlier suggestion of fitting an enclosure with main switch and 2 RCDs to feed each row of fuses would be much simpler.
It wouldn't take much to chop that neutral bar in two.
 
In ripping it apart and rebuilding it with MCBs etc you are pretty much building your own DB for which I would imagine you'll have to deal with CE marking and lots of statutory regulations.

My earlier suggestion of fitting an enclosure with main switch and 2 RCDs to feed each row of fuses would be much simpler.
It wouldn't take much to chop that neutral bar in two.

I'm not sure you would have to justify such a build to any particular standard, but it would certainly be a PITA ... lol
 
The trouble is you probably wouldn't find out for sure until the judge is telling you all about it as you stand humbly in the dock.

Not sure about that. I've never really thought twice about mounting din rails carrying switchgear in metal enclosures, or even adaptable boxes. My thinking would be that as long as you complied with the rules for enclosures in BS7671 then all would be well with the world. I can't think of any aspect of that enclosure that would cause me concern in mounting equipment inside it. There is not much at all to an enclosure that you purchase specifically for this purpose.

Or am I just being a bit eager ?
 
Been out to a family member that has just brought a new property.

He would like a few new sockets the usual. Open the cupboard under the stairs to find this.

epatu7e7.jpg


anu7y2up.jpg


ru9u3yvu.jpg


7a8y7ete.jpg


All earthed metal conduit. A real piece of workmanship just seems a shame to take it all out. Would be nice to keep some of it but where to start!

The lack of rcd protection being the main problem for any additions.

What would you guys do?
I was considering a second board and running new circuits out or possibly using the conduit to pull new cables through and then floor boards up and new rings?

All advise welcome!

I think I would install a Lathe in the living room and a Milling Machine in the dining room and start a nice little engineering company.
 
I have no problem with mounting din tails and all sorts of stuff in an enclosure.

But to make a domestic CU you would also have to make and fix an internal cover to allow the untrained to reset a breaker without exposing live parts.
Yes it can be done, but at what cost in time and materials?
 
I have no problem with mounting din tails and all sorts of stuff in an enclosure.

But to make a domestic CU you would also have to make and fix an internal cover to allow the untrained to reset a breaker without exposing live parts.
Yes it can be done, but at what cost in time and materials?

Yep true.... would love to see it done though
 
Yep true.... would love to see it done though

I wouldn't though, I think butchering old equipment to make it into something else is wrong. If you do that then it is no longer the thing which you are trying to preserve.

The neutral fused main switch has got to go anyway, so might as well do the modifications there. Or else take the board out and replace with a new metal CU with SPSN RCBOs
 
I wouldn't though, I think butchering old equipment to make it into something else is wrong. If you do that then it is no longer the thing which you are trying to preserve.

The neutral fused main switch has got to go anyway, so might as well do the modifications there. Or else take the board out and replace with a new metal CU with SPSN RCBOs

There's an echo around here.
 

Reply to Where to start. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So I'm starting out a new rig and I'm fresh out of college with my level 3 without any experience and I think that I need to still have the...
Replies
5
Views
727
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
927
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
987
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
693
Hello, I have 50 ft of corrugated pipe buried between my house and a pool shed. I placed it where I knew future landscaping would make it very...
Replies
3
Views
486

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock