Discuss Which is the DNO earth block? PME in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
34
Hi All I would be interested to hear your opinions on this situation:

It's a property which used to have the electricity meter in the middle of the house, the consumer unit is still there and there is still a cut out with a 100A fuse in it, a neutral earth block and a small label that says it is PME. Some time in the past there was a service alteration and now there is an outside meter box with the meter and another cut out. The cable between the cut outs is the original electricity board service cable all made off correctly and in good condition. There is a 6mm earth cable between the two cut outs and the 16mm main earth and 10mm bonds to gas and water all go to the original cut out in the middle of the house.

So the question is should the main earth and gas and water bonds go to the new cut out or is it OK where they are?
 
Have you carried out the adiabatic equation to see if a 6mm earthing conductor is adequate? In an ideal world for PME/TNC-S the earthing conductor would be a minimum of 10mm. This is the distributors equipment though so they must of deemed it to be adequate. What work are you conducting at this property?
 
Don't you just love the DNO, they can do whatever they want!! That really sounds much more like a DIY move of supply!

Because of the arrangements that are in place it is very clear, presumably, that the supply comes in from outside.
The presence of the NE block at the middle of the house indicates that the cable from outside to inside is not part of the consumer's installation, it is the DNO's supply cable irrespective of the fact that they have provided two cut outs.
Therefore the earthing and bonding are correctly located close to to the origin of the installation and connected to the supply company's earthing arrangement.

The size of that earthing arrangement is odd as said above, however presumably the neutral core of the supply cable is providing the earth up to that point as well, so it should be OK, but there is nothing you can do about it anyway.
 
Sounds like the authority have just cut the original supply and diverted via the outside meter arrangement. Strange.

What have they done with the original meter arrangement....still in place, bypassed straight from the cut out or what ?
 
I don't have any photos, the tails coming from the original cut out now feed the CU and the meter has been moved to the outside meter box. The neutral and earth are still linked at both points.

The work is to change CU so I am wondering whether to allow for running new earth cables back to outside meter box which is 15 metres away and very awkward route.
 
I have had this exact setup before where the DNO just fitted a red link cutout at the old meter position. That one clearly had the PME terminal at the original position
 
They might have the answer but you would be lucky to find out categorically from them in less than the age of the universe.
Still, worth a try.

From my point of view if the neutral and earth are combined then this is the suppliers cable as it against the ESQCR regulations to have a combined neutral earth in a consumers installation.
8 (4) A consumer shall not combine the neutral and protective functions in a single conductor in his consumer’s installation.
 

Reply to Which is the DNO earth block? PME in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
629
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
3K
Good morning all, I am currently working on a House in Multiple Occupation (HMO) consisting of 10 flats, with three parking spots equipped with...
Replies
9
Views
548
  • Locked
My house was built in the 1930s, The fuse in my service cut out is 60Amp and the wire coming from the street has a 16mm2 copper core(easy to see...
Replies
12
Views
582
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock