Discuss Which unit/enclosure to house upfront RCD? in the UK Electrical Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Reaction score
5,607
Evening..

Just looking at a CU change on a TT. I'd like to put a 100mA S type RCD before the CU. Is a 2 way (4 spaces) amd 3 metal board my only option? Its a bit big!
 
It's easily arguable that a self-contained RCCB within an enclosure is not a "similar switchgear assembly" to a distribution board. For a start it provides no overcurrent protection. Therefore it isn't clear that it must be made of ferrous metal, e.g. steel.
 
If all circuits are 30mA protected why bother with an S type at all, just use an appropriate gland for the tails

Backup fault protection in case the 30mA doesn't operate.
I realise that everybody always follows the test quarterly instruction so there's minimal chance of them failing to trip when needed, but just in case the user of the installation forgets to keep up to date with pressing the test button a backup protective device might help.
 
I realise that everybody always follows the test quarterly instruction so there's minimal chance of them failing to trip when needed, but just in case the user of the installation forgets to keep up to date with pressing the test button a backup protective device might help.
If you said that with a straight face, I wouldn't wanna play poker against you! :)
 
Why not replace the main switch in the board with an S-type?

Could do, but at present the tails go into a Henley block and then to the CU, so it seems opportune to change to the RCD. Plus it will provide isolation for the board when required, plus give RCD protection for the one in a million time the tails come loose and touch the metal CU (TT).

It's easily arguable that a self-contained RCCB within an enclosure is not a "similar switchgear assembly" to a distribution board. For a start it provides no overcurrent protection. Therefore it isn't clear that it must be made of ferrous metal, e.g. steel.

Will be interesting to see if there are any more thoughts on this. I don't think there's going to be a right or wrong answer, just confusion!
 
Could do, but at present the tails go into a Henley block and then to the CU, so it seems opportune to change to the RCD. Plus it will provide isolation for the board when required, plus give RCD protection for the one in a million time the tails come loose and touch the metal CU (TT).



Will be interesting to see if there are any more thoughts on this. I don't think there's going to be a right or wrong answer, just confusion!


But the chances are you would have to house the RCD in a metal enclosure anyway so you would have just as much chance of that happening to the enclosure for the RCD. Imo thinking you would get away with housing the RCD in a separate insulated enclosure is wishfull thinking when it comes to an assessment from your scam. I would use a Hager design 30 board with the tail clamp, nylon tail gland kit, clip the tails entering the board and change the main switch for a 100mA time delayed RCD. On top of that I would ditch those Henley blocks and replace the tails from the new CCU to the meter.
 
But the chances are you would have to house the RCD in a metal enclosure anyway so you would have just as much chance of that happening to the enclosure for the RCD. Imo thinking you would get away with housing the RCD in a separate insulated enclosure is wishfull thinking when it comes to an assessment from your scam. I would use a Hager design 30 board with the tail clamp, nylon tail gland kit, clip the tails entering the board and change the main switch for a 100mA time delayed RCD. On top of that I would ditch those Henley blocks and replace the tails from the new CCU to the meter.

I think that's all pretty spot on Lee, cheers :)
 
It's easily arguable that a self-contained RCCB within an enclosure is not a "similar switchgear assembly" to a distribution board. For a start it provides no overcurrent protection. Therefore it isn't clear that it must be made of ferrous metal, e.g. steel.[/QUOTE]

I like the way even when speaking normally we sound like a regs book :)
 
I would fit the RCD in one of those enclosures that the REC type isolators come in and list the plastic enclosure as a deviation from the regs as I would deem it to be a justified deviation in my professional opinion. Obviously using a good quality RCD and terminating it securely to prevent loose connections etc.
 
Just to add my two pennneth and further this debate. I've asked my scheme - Elecsa - re housing RCD in insulated enclosure. Their interpretation is that a upfront RCD would need to comply with 421.1.201. When I fitted a Wylex A3 CU, it had a set of pics showing various installations, one of which showed a recommended install for a TT with a plastic enclosure for upfront S type. When I rang Wylex technical asking if they could explain, they batted me off to some sales guy, who said it was the lesser of two evils.

Think all will have seen the Elex at Harrogate 15 vid, and I seem to remember this was mentioned, with a 'we waiting further guidance' or something like that.

IMO is fairly easy to install a S type in a metal enclosure, using Wiska tails gland or similar & 6181y cable, which should make the possibility of shorting incoming mains almost impossible .

It's pretty damn annoying though, that prior to A3, you would have been strung up using a metal CU with a TT supply!
 
But the chances are you would have to house the RCD in a metal enclosure anyway so you would have just as much chance of that happening to the enclosure for the RCD. Imo thinking you would get away with housing the RCD in a separate insulated enclosure is wishfull thinking when it comes to an assessment from your scam. I would use a Hager design 30 board with the tail clamp, nylon tail gland kit, clip the tails entering the board and change the main switch for a 100mA time delayed RCD. On top of that I would ditch those Henley blocks and replace the tails from the new CCU to the meter.
You been watching them videos I see!
 
you could enclose it in this:

depositphotos_6532539-Safe-in-stainless-steel.-Bank-Vault..jpgtotally fireproof.
, vandal proof, and Electrical Trainee resisatnt.
 
Pathetic. I know some guys who can get into that no problem, over the course of a bank holiday weekend.
Although they are a bit ill-disposed at the mo.
 
Last edited:
Have you investigated whether PME is available?
Pretty rare that it's not these days and I'd go for that every time over a TT.

No I haven't. What sort of price do they charge? Do they charge? Expect it varies between DNO's?
 

Reply to Which unit/enclosure to house upfront RCD? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I've done some work in a house, I used an existing 10mm cable on a B40 MCB to supply a 2 way consumer unit to control a heat pump and...
Replies
1
Views
1K
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
864
Have an existing old client with what's best described as a sprawling small-holding of a property. There's an armoured external supply which...
Replies
25
Views
3K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock