Discuss White FP external use in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

H

Happygrumpysparks

Hi,

Had a look at a job today and noticed external lighting had been wired in white FP, clipped to wall surface.

I informed them mechanical protection must be provided and they insisted the board had RCD protection and it wasn't required.

Anyone else seen this before.
 
mechanical protection would only be required if there was a danger of the cable suffering impact damage. what's also relevant is that FP will degrade due to sunlight etc.
 
Was working on the roof of a huge department store a few years ago and miles of white fp was on trays to the ac units, most of the sheath was dust on the floor.
 
Interesting. According to the manufacturer, FP200 can be used externally. From the manufacturer's data sheet:

Sheath

Robust thermoplastic low smoke, zero halogen and reduced flame propagation outer sheath. Standard colours white and red with bespoke colours available to special order. Suitable for outdoor installation with exposure to normal daylight UV.

http://www.fpcables.co.uk/FP200_Gold_Prysmian_2.pdf

So, as per Telectrix's first sentence, mechanical protection only required if likelihood of impact damage (or some other external influence).

Is it confirmed Prysmian FP200? Or perhaps some other "equivalent"?
 
Interesting. According to the manufacturer, FP200 can be used externally. From the manufacturer's data sheet:

Sheath

Robust thermoplastic low smoke, zero halogen and reduced flame propagation outer sheath. Standard colours white and red with bespoke colours available to special order. Suitable for outdoor installation with exposure to normal daylight UV.

http://www.fpcables.co.uk/FP200_Gold_Prysmian_2.pdf

So, as per Telectrix's first sentence, mechanical protection only required if likelihood of impact damage (or some other external influence).

Is it confirmed Prysmian FP200? Or perhaps some other "equivalent"?

Thanks for everyone's replies.

Ive not confirmed what exactly, but I expect it wasn't Prysmain fp200 and more likely a cheaper equivalent going by the quality of light fittings.
 

Reply to White FP external use in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I've had a search, and found an old thread from 2016... but was wondering about modern views on this situation. I've come into possession of...
Replies
5
Views
356
I have a job coming up where I likely need to replace old twin and earth (imperial size) feeding one, perhaps two flats in a 3 storey converted...
Replies
20
Views
2K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
863
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
Hi guys, I've got a job where I'm installing dado trunking on the floor of an office for sockets and data. Some info on job - In total I will be...
Replies
18
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock