Discuss Who does just a Zs when carrying out a periodic on a lighting circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

N

nickblake

Just answered a question on another post ,and it dawned on me , yippee the brain kicked into gear , i have read on loads of posts that people say doing an inspection just calculate the R1R2 by doing a Zs and taking away the Ze , i have never liked this method and heres a reason why , supplimentary bonding !!!!! you go into a house you do an R1R2 test you get a reading if there are any open circuits it shows up and it can be rectified , so what happens if the install is up to 16th edition all supplimentary bonding is in place ,3/4 the way through the lighting circuit there is a bathroom with an electric shower , you find the last on the run bedroom next to the bathroom quick Zs all ok , heres the scinario , the cpc's have have been cut off at the first light switch , metal clad switches and light fittings , so you test the last on the run get a good Zs reading fill in the sheet calculate the R1R2 and walk away ,so what if the supplimentary bonding has been installed between the shower and the light as it was in the 16th edition ,you then will have a reading which is false and potentially leave the entire un earthed circuit thinking its ok , so the moral of the thread is R1R2 Insulation and Zs simples easy to see the supplimentary bonding and and not put 2 and 2 together , thank you malcom for kicking my brain into gear on this one just a comment he made made me think :devilish:
 
R1&R2 should never be calculated from Zs and Ze. It can only be calculated from resistivity, factors and length.
I believe that it's never been written down as an acceptable method, if it has I would like to see it.
 
got my arse kicked by Elecsa when i calculated on my first assessment ZS-ZE... never did it since and luckily i never got reassessed as it went down as observation only!
 
Totally agree widdler but you see posts on here saying just do a Zs when inspecting , and my post is just there to high light why it should never be done , yes to calculate the Zs but not to back calculate ,
 
Totally agree widdler but you see posts on here saying just do a Zs when inspecting , and my post is just there to high light why it should never be done , yes to calculate the Zs but not to back calculate ,

Ha, let them try it in a decent sized industrial installation, you can almost end up with a negative R1+R2 once the parallels have taken effect!
 
On a new or altered installation there is no excuse not to carry out the dead test as well as live tests.

On a PIR..... well......errrrr....
 
Totally agree widdler but you see posts on here saying just do a Zs when inspecting , and my post is just there to high light why it should never be done , yes to calculate the Zs but not to back calculate ,

If you see any of them pop up again mate can you refer them to this thread, that is advise we have to eliminate from here.
 
yep i see what you are saying jason , one i will remeber did a R1R2 on a lighting circuit tested out ok , but the was something not quite right , found out that half way though the circuit the polarity changed then changed back again , 4 lights had an incorrect polarity so now i do tend to do an R1R2 at every lighting point
 
I don't generaly measure or record R1+R2 on PIRs, unless the power is off.
I just conduct a Zs test at each fitting to prove continuity, and operate the associated switch to prove polarity.
 
I don't generaly measure or record R1+R2 on PIRs, unless the power is off.
I just conduct a Zs test at each fitting to prove continuity, and operate the associated switch to prove polarity.

The test is 'continuity of protective conductors' and there is no requirement to have a value, only to prove continuity.

If your 'buzzer set' meets the requirements for continuity testing (current and voltage) then you're there.

Using EFLI only as a continuity of protective conductors test will probably open up a few more pages of debate....
 
I don't generaly measure or record R1+R2 on PIRs, unless the power is off.
I just conduct a Zs test at each fitting to prove continuity, and operate the associated switch to prove polarity.

The key thing there being that you don't record calculated values.
I take it you don't do verification of voltage drop then?
 
Totally agree widdler but you see posts on here saying just do a Zs when inspecting , and my post is just there to high light why it should never be done , yes to calculate the Zs but not to back calculate ,

There are two instances on a PIR where it IS acceptable to omit R1+R2 and just carry out a Zs.

1. Where a previous full schedule of test results is available to the inspector it is permitted to carry out a Zs test and compare to previous recorded results. If the measured Zs is the same or very close to the previous recorded Zs it is reasonable to assume the R1+R2 will also be the same and omit that test, if the results were not substantially the same the R1+R2 would need to be verified.

2. Where it is agreed with the client that an R1+R2 test should not be carried out in order to minimise disruption to essential supplies.

In both instances it should be stated on the extent and limitations section that R1+R2 tests were not carried out and the reasons why.

It is quite wrong to state that an R1+R2 test should always be carried out on a PIR
 
i have to on a PIR software goes nuts if i dont fill it in , i do like to see what the readings are on an R1R2 test then i can get an approximate idea of what the Zs reading should be and take into account of parralell earth paths etc , if i dont do it the testing just doesnt feel right i know it sounds daft when you use a method for so many years , like changing from a manual gear box to an automatic i suppose
 
i have to on a PIR software goes nuts if i dont fill it in , i do like to see what the readings are on an R1R2 test then i can get an approximate idea of what the Zs reading should be and take into account of parralell earth paths etc , if i dont do it the testing just doesnt feel right i know it sounds daft when you use a method for so many years , like changing from a manual gear box to an automatic i suppose

I know what you are saying,but there are plenty of situations when doing a PIR when it just isnt practical,or entirely neccessary. Technically the DB should be isolated when R1+R2 testing...which can take a considerable time on a large DB with multiple circuits.....it just may not be feasible in a typical working environment.
 
Whilst I don't agree with everything within GN3, and I accept that it is just guidance based on someones opinion.
As far as I'm aware GN3 suggests using an EFLI test as being the most practical method of proving continuity.
 
Whilst I don't agree with everything within GN3, and I accept that it is just guidance based on someones opinion.
As far as I'm aware GN3 suggests using an EFLI test as being the most practical method of proving continuity.

It does indeed.
 
LOL sorry guys who was it on here who told me off for doing live tests and that an nic bod said you were not allowed to to live tests any more due to health and safety , now that one will throw a spanner in the works lol
 

Reply to Who does just a Zs when carrying out a periodic on a lighting circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, I've just had some electrical work completed in the bathroom; I've recently refurbished the bathroom, replacing the old electric shower with...
Replies
39
Views
8K
Summary (TL;DR) Several lightbulbs in my home supplied by one circuit breaker dim over time and go out in about a year. Right now, the ceiling...
Replies
0
Views
734
I have been asked by Trading Standards to carry out a report on some electrical work installed by another company (5 years ago). The 'new' wet...
Replies
31
Views
3K
Afternoon all. Bear with me on this one... Despite having been involved in the electrical industry for many years, I'm only just about to embark...
Replies
15
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock