So, I was messing around yesterday with some old testers I have laying around to see if they still work
I found my dads old Robin MFT and noticed something I have never noticed before
When you test of the EFLI setting put live and neutral probes on a switch or socket but don't connect the earth probe you get 120-130 ish volts.
Soon as you clamp the earth lead on it jumps back to 230-240V
Why is this ?