Lol nah i'm a trainee without an employer, trying to get as much info as i can to the many hundreds of questions i have ?I can sense a picture coming.
Discuss Why do we do it the way we do in the UK? in the UK Electrical Forum area at ElectriciansForums.net
Lol nah i'm a trainee without an employer, trying to get as much info as i can to the many hundreds of questions i have ?I can sense a picture coming.
That's what i woulda thought - is it true that you're only allowed one radial per 50sqm area? I've heard this said but struggling to find the rule written down.my thinks......average house.RFC for kitchen, rest of sockets on 2/3 20A radials.
There is no rule as such, just some guidance for "typical" usage. From memory it is 50m^2 for 20A radial, 75 for 32A radial and 100 for 32A RFC.That's what i woulda thought - is it true that you're only allowed one radial per 50sqm area? I've heard this said but struggling to find the rule written down.
I would agree. Some prefer 4mm radials but that is marginal if much thermal insulation, and by 6mm it is hard to wrnagle or fit pairs in to socket terminals..I thought RFC for the kitchen just because of the load being drawn if eg toaster, kettle, dishwasher and washing machine are all on at the same time.
Yes, they are nice boxes, and he's very flexible.By the way, SBS make one....
I've been thinking about trying one when I find the right job for it.
CEF appear to do a 32mm one, though the image does not seem to match as it does for the 40mm one:Yes, they are nice boxes, and he's very flexible.
Also does some nice glands. The 25mm tail set he does fits in a 32mm hole, and there's an adapter if yo have a 40mm hole. The last one I got from the wholesaler (CEF) was 40mm an by the time you added an adapter down to 32mm it was a horrible monstrosity.
As I understand it, the double pole RCBO's only monitor the Phase side, the neutral side is just dragged along on a fault condition, so as you say it does break both.
You can get DP RCBOs in single width, like the compact Wylex, Crabtree, and fusebox RCBOs so they take no more space then traditional UK style MCBs.Its all DP 2-mod rcbos here
Takes up more space ,.main boards are always at least ,2-row
Better job on an rcbo board to be breaking both live poles for a fault I reckon