True and I absolutely agree with maximising selectivity for minimising inconvenience during a fault and facilitating easy fault finding, but I was under the impression that AFDD protection HAD to be per circuit?Probably for the same reason RCBOs are preferable to split RCD boards... we should be looking to minimise disruption in the event of a fault. Plus, it makes fault finding a hell of a lot easier if you know which circuit you're looking at to begin with.
Thanks for this SparkyChick, So its confirmed then, the regs definately want us to install per circuit, but I just wonder why? Is it purely to do with Selectivity or is there a more practical/technical reason for it?And.....
421.1.7 Arc fault detection devices conforming to BS EN 62606 are recommended as a means of providing additional protection against fire caused by arc faults in AC final circuits.
If used, an AFDD shall be placed at the origin of the circuit to be protected.
NOTE: Examples of where such devices can be used include:
• premises with sleeping accommodation
• locations with a risk of fire due to the nature of processed or stored materials, i.e. BE2 locations (e.g. barns
woodworking shops, stores of combustible materials)
• locations with combustible constructional materials, i.e. CA2 locations (e.g. wooden buildings)
• fire propagating structures, i.e. CB2 locations
• locations with endangering of irreplaceable goods.
What SC saidFrom the regs:-
532.6 Arc fault detection devices (AFDDs)
Where specified, arc fault detection devices shall be installed:
(i) at the origin of the final circuits to be protected, and
(ii) in AC single-phase circuits not exceeding 230 V.
Very good point. At the origin of the circuit is positioning, not Selectivity Light bulb moment!RCD's are also at the "origin of the circuit" I don't take that as necessarily individual to each circuit. It may be more to do with the operation of the device itself, but cannot see why split load AFDD's would not work
Reply to Why does AFDD protection need to be per circuit? in the UK Electrical Forum area at ElectriciansForums.net