Basically it is ohm's law, though for large cables it is slightly more complicated as both resistance and inductance (i.e. impedance) are significant.

Ib is the design current, so what the circuit is expected to carry. That might be a fixed load, or it might be the maximum for a set of sockets, etc, determined by the supply breaker rating. At that current the impedance of the cable results in a drop in voltage which may or may not be acceptable, so the factor are:
  • Cable impedance per unit length (basically inversely related to the size of the cable)
  • Cable length
  • Design current Ib
  • Nominal voltage Uo

The nominal voltage is a factor as most specifications for VD give it as a percentage of the nominal supply. Hence very low voltages like 12V are impacted far more by a given drop than typical AC supplies at 230V, etc.
 
At that current the impedance of the cable results in a drop in voltage
Now you put it like that makes absolute sense, really should have known. Im becoming complacent doing the formulas / cable calcs that the principles are eluding me. I hope I dont go bald ! Thanks for the refresher !
 

Reply to Why does design current affect vd in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Sorry if this has already been posted before, but it's not something I can find a definite answer to. Does anyone know if passing the 2396 Design...
Replies
2
Views
639
Hi, go easy on me please, I've just returned to the trade, well I am about to, I received my Gold Card last Thursday. I've been gen'ing up for a...
Replies
4
Views
886
Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
11
Views
374
Hi Doncaster EV ultra cable: Does anyone know what the current capacity of these cables is given particular reference methods? The spec sheet...
Replies
3
Views
2K
Hi we are replacing light fittings in our home. Im confident with the fitting aspect, but have run into doubt in making the right choice of...
Replies
2
Views
488

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock