Discuss WHY ISNT THERE A NEUTRAL WIRE IN THREE PHASE in the UK Electrical Forum area at ElectriciansForums.net

Why the main three phase doesnt have a neutral wire before reaching a stepdown transformer, how does electricity form a loop back to its source
You actually create your neutral in the load side of the transformer. The primary side doesn’t require a neutral in some transformers.
 
With a three phase system the current from any one phase can return via the other phase(s) depending on the load. So if your load does not need a neutral point (such as a delta-connected motor or transformer primary) you don't need a natural cable! And so you can save significant cable cost on the distribution side.

Once you get to the low-voltage side for general purpose use then it is a convention to provide the neutral. in the UK/EU that is very standard (230V L-N /400V L-L) via a star-connected transformer secondary ('wye' in USA parlance).

The high voltage sending end usually has the neutral mid-point earthed. Sometimes via an impedance designed to control fault currents, etc, and sometimes by means of an earthing transformer if the source lacks a star point (such as an alternator, delta-connected transformer secondary, etc)

 
Last edited:
Why the main three phase doesnt have a neutral wire before reaching a stepdown transformer, how does electricity form a loop back to its source
On a 3 phase Delta system you don’t have a neutral on the primary side of your transformer. I have worked in a lot of plants with a 3 phase delta system and if something goes to ground it will not blow a fuse or trip a breaker. That’s why most plants with a delta system they usually have 3 lights with each light is phase A, phase B or phase C. If one light is out and the other 2 lights get brighter then they have a grounded phase.
 

Reply to WHY ISNT THERE A NEUTRAL WIRE IN THREE PHASE in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Having a challenge understanding the concept behind why when you measure across line and neutral (live circuit) using voltage indicators we have...
Replies
25
Views
2K
BIG place OK lots of electrical bits. but one on a 3 phase Radial is tripping its RCCB so i check the wiring making sure its tight and it has...
Replies
5
Views
336
Anyone come across this before? I was asked to do a Zs on a 3ph surge device; L1 was around 6 ohm, L2 & L3 around 0.11. Wired in singles from a...
Replies
1
Views
436
I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
842
Hello all, I signed up here for a little help. I bought a 3 phase bandsaw and went down the rabbit hole of VFD’s etc. ‘The motor is 3 phase 400v...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock