If you read the full article, it makes a case that by using the adiabatic correctly for 16mm you can actually use it for a 100A DNO fuse (BS1361) due to the time/current characteristics versus adiabatic on the cable.

Guess ultimately it comes down to 1) knowing your trade properly 1.1) understanding what the regs/maths implied actually mean and 1.2) a good old fashioned dollop of experience.

And I guess that now counts an awful lot of people out!
 
The DNO's local to me have required 25mm² tails for a long time now the last time I can remember using 16mm² tails was around the early eighties

On all the sites I've seen where the meter has been changed recently the cut out to meter tails have been changed to 25mm²

May be the thinking is "what will do a lot will do a little" also as we all know there is no chance of the DNO's fuse blowing at any where close it's rated value so the larger tails will cope better with the potential overload beyond the fuses value
 
Likewise, and I wouldn't dream of using anything other than 25mm+ just to not get the grief and the argument, but it does make you think that there are an awful number of CU replacements going on where the tails are being replaced without any technical justification.
 
And how much is a couple metre of 25mm tails?tenner?Hardly a great expense for a piece of mind and future proofing
 
Last edited by a moderator:
That's exactly my complaint. The 'powers that be' simply add a little more contigency into everything because that's easier than updating the 19th century technology underpinning today's wiring regs. Current MCB and RCD 'technology' could be replaced with something vastly more effective and accurate, but the entire industry is geared to churn out the things for a couple a quid apiece, and no one wants to invest in developing and marketing alternatives. My other beef ( oh, dear, second rant of the day coming on) is that while cables have got thicker (and total loads have generally gone down) the casings for CU and isolators, etc have got thinner and cheaper. It won't be long before we left with a bunch of breakers wrapped up in a 'plastic bag', wafting around in the air on top of a couple of rigid meter tails.
 
Likewise, and I wouldn't dream of using anything other than 25mm+ just to not get the grief and the argument,

That's it in a nutshell for me. With the proviso that as long as you have the knowledge (or the professionalism to want and gain the knowledge) as to why what you're fitting isn't strictly necessary then it's OK.

A similar situation IMHO to the "it must be RCD protected, and if it is all's well in the world". I've been to quote on a couple of jobs in the last few weeks where the customer has been told "It must have an RCD" or "You need a new CU" when neither is true. I just can't make up my mind if it's an excess of greed, or a shortage of knowledge driving them to tell customers such things.
 

Reply to Why oh why 25mm meter tails? in the Australia area at ElectriciansForums.net

Similar Threads

D
Hi, i've ran a radial into an extension. There are no spare ways on the existing 3036 DB. All the circuits are doubled up in fuse holders anyway...
Replies
17
Views
10K
don Logan
D
hi guys got a cu to change from the meter to old cu there is 16mm tails with 10 mm earth as the meter is locked off with crimps & wire what...
Replies
6
Views
10K
M
Hi all, very sorry to bother you with triv. I am in the process of sorting out some pretty shocking electics in a house that has been bodged at...
Replies
0
Views
3K
mbga9pgf
M

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock