Discuss Why oh why 25mm meter tails? in the Australia area at ElectriciansForums.net

That's it in a nutshell for me. With the proviso that as long as you have the knowledge (or the professionalism to want and gain the knowledge) as to why what you're fitting isn't strictly necessary then it's OK.

A similar situation IMHO to the "it must be RCD protected, and if it is all's well in the world". I've been to quote on a couple of jobs in the last few weeks where the customer has been told "It must have an RCD" or "You need a new CU" when neither is true. I just can't make up my mind if it's an excess of greed, or a shortage of knowledge driving them to tell customers such things.
well any work we do (my boss n i) that requires additional protection by means of RCD....we just fit a garage board...fed either from a spare way in the existing c/u.......or henley...either way you dont need to be fitting a complete new c/u as firstly you will need to inspect and then test the whole install again...( a can of worms)....and secondly only work you do needs to comply with the current edition of BS7671.....
 
I havent read all the posts!! but when I did my 16th edition and test and connect course years ago I was told that even though you may have a 60/80 Amp head at the time, the DNO may upgrade their service to 100 amp, therefore its prudent to fit 25mm tails.
 
I havent read all the posts!! but when I did my 16th edition and test and connect course years ago I was told that even though you may have a 60/80 Amp head at the time, the DNO may upgrade their service to 100 amp, therefore its prudent to fit 25mm tails.
and if you do your diversity calcs for the CU?.....100% of the highest load then 40% of the rest combined?..probably wont be 100A....and dont forget you can clamp it n all....bet you dont get anyware near 80A never mind 100A....
 
Totaly agree Glennspark, if you do get near 100A in a domestic setting I would hate to see what the quaterly bill was!!! and 25mm just dont bend as easy as 16mm and im sure the design of most the domestic stuff aint designed for 25mm, all the main switches seem to destort and argue.. but nothing a hammer cant fix "I will get that tail in":hammer:
 
well any work we do (my boss n i) that requires additional protection by means of RCD....we just fit a garage board...fed either from a spare way in the existing c/u.......or henley...either way you dont need to be fitting a complete new c/u as firstly you will need to inspect and then test the whole install again...( a can of worms)....and secondly only work you do needs to comply with the current edition of BS7671.....

I recently had to do work on a shower circuit and was going to do a two way wylex with main switch and 40A RCBO. Instead though, I discussed with the client and agreed to fit a 5 way board. My reasoning was that at any point in the future they could have an individual circuit tested and dropped in AND protected with a 30mA RCBO. If there was any fault finding to be done then there would be no interuption to their installation.
 
I've wondered about this as well. I've got a CU change coming up in a house with 16mm tails. I am tempted to just fit 25mm tails from the meter to the CU because it's a no brainer, it's not that much hassle and is probably the safest option from a part P assessment point of view, even if it is not really necessary from an electrical point of view, but the only thing that puts me off this approach is DNO seals on the meter connections. How do most sparks deal with that?
 
well you can always replace tails but how about showing your assessor how you do diversity calcs...for current using equipment/connected loads as well as C/Us.....that would be good wouldn`t it....;)
 
but the only thing that puts me off this approach is DNO seals on the meter connections. How do most sparks deal with that?

do the maths and leave the 16mm in if ok.

if dno want to come along at a later date and up to 100A fuse thats their look out just make sure you comply with your work and leave them meter seals alone!!
 

Reply to Why oh why 25mm meter tails? in the Australia area at ElectriciansForums.net

Similar Threads

D
Hi, i've ran a radial into an extension. There are no spare ways on the existing 3036 DB. All the circuits are doubled up in fuse holders anyway...
Replies
17
Views
10K
don Logan
D
hi guys got a cu to change from the meter to old cu there is 16mm tails with 10 mm earth as the meter is locked off with crimps & wire what...
Replies
6
Views
10K
M
Hi all, very sorry to bother you with triv. I am in the process of sorting out some pretty shocking electics in a house that has been bodged at...
Replies
0
Views
3K
mbga9pgf
M

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock